dlt27

-
Joined
Jul 4, 2011
Messages
196
Reaction score
30
Sorry this is a long one!
I have been carrying out testing and Inspecting for about 10 years now, but haven't come across what I found at my Mum and Dads house. I rewired it about 12 months ago. It is an old stone house and was a nightmare to do.(It's a TT system fed off overheads and a split load MK board with an RCBO on the smokes.
I got a phone call yesterday with my mum saying that Western Power had turned the power off and when they put it back on half the circuits wern't working. I haven't dived into it yet because I haven't had time and also I thought I'd put it out to you lot to see if you had any ideas.
I went around there turned of all the circuits and reset the (bad)RCD then when I put the kitchen sockets on and it tripped. I thought faulty appliance somewhere tried fridge and it tripped the RCD then tried kettle and it did the same. Tried unplugging everything then tried one at a time however then couldn't get it to trip. I thought adding a load to the circuit was obviously finding the fault and I would megger it the next day because didn't have tester.
I went around this morning and Dad said basically anything they turned on tripped the (Bad)RCD . Sometimes the lights, sometimes the immersion, however it was totally intermittent. The funny thing was even circuits on the 2nd (Good)RCD was tripping the 1st (Bad)RCD ie cooker, but not all the time.
I tried all trip tests on what I thought was the (Bad)RCD and couldn't get it to trip, not even with a ramp test. Test button worked though. I thought I've got it. I tried same tests on 2nd (Good)RCD and it all tripped correctly, however when I tripped it I found it tripped the (Bad)RCD and also the RCBO I have got on the smokes. So basically what I thought was the good RCD tripped the 2 RCD's and the RCBO. I also found the test button on the faulty (Bad)RCD also tripped the RCBO, but didn't trip the good RCD. I've checked all neutrals of RCD's to check not mixed up or in wrong neutral bar etc. All is correct. I've checked neutral coming in to property is neutral etc and found PFC to be 0.21 live to neutral. I am going tomorrow to carry out a proper test ie. Disconnect all Neutrals and Lives of circuits and then try RCD tests, meggering etc.
To summarise what I can't understand is how all circuits in the board are tripping the bad RCD and RCBO like a borrowed neutral and why only intermittantly. Also why does so called good RCD trip bad RCD and RCBO when carrying out tests, yet bad RCD won't trip when tested.
The final thing is I don't understand why this as only happened since Western power turned the power back on, but I can't find anything wrong with supply. Any ideas would be much appreciated.
 
However would of thought it would not reset not be intermittent unless the n-e voltage is constantly changing

Which it is, usually increasing with load on both your own installation and others nearby. It's caused by voltage drop in the DNO's cable.

Also surely it would not affect the rcd not tripping when tested.

Another classic symptom of N-E faults as the fault can sometimes bypass some of the test current around the RCD.
 

Reply to Really strange RCD happenings in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
715
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
3K

Similar threads

Exactly. I was going to ask on the earthing once he clears this boiler fault (suspect on internal component). OP mentions oil boiler but makes no...
2
Replies
19
Views
797
  • Question
Yes I touched on diverted neutrals when I went over guidance note 3 the first time but I’m doing a second round and going between all books whilst...
Replies
9
Views
506

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top