Hi,
I went to a property yesterday very large upstairs flat. Meter & service head in the hall way down stairs, tails into an 30ma rcd then travel over 4m to cu upstairs in the cupboard. Cu is dual rcd 30ma. Problem is probably obvious, when a light pops the rcd trips downstairs and is a hazard as no light when coming downstairs. Flat has recently been rewired, TT earthing system. First of all there is no discrimination it will be pot luck which rcd trips, there should also be a switched fuse next to the meter as tails over 3m.
Tails are not surface mounted & travel through the fabric of the building. If it was TN i would say, use 25mm Swa as the tails, armour earthed & also a seperate core for an earth. (and no rcd at the intake).
Q.1. Would this be correct & acceptable?
Q.2. If the tails were surface mounted in a TN installation i would just use standard tails 25mm (no rcd), would this be correct & acceptable?
However the installation is TT, therefore could the 30ma rcd be changed for 100ma s type? And could the tails be left? (The tails may not be deeper than 50mm in the building fabric.) Would the tails have been better installed in s.w.a with 100ma s type front end.
Is there a better way of doing this?
Sorry quite a few questions there for a friday morning. There are 3 of us having a debate over this. Maybe the chaps who installed it, should have had this debate :25:
Cheers
I went to a property yesterday very large upstairs flat. Meter & service head in the hall way down stairs, tails into an 30ma rcd then travel over 4m to cu upstairs in the cupboard. Cu is dual rcd 30ma. Problem is probably obvious, when a light pops the rcd trips downstairs and is a hazard as no light when coming downstairs. Flat has recently been rewired, TT earthing system. First of all there is no discrimination it will be pot luck which rcd trips, there should also be a switched fuse next to the meter as tails over 3m.
Tails are not surface mounted & travel through the fabric of the building. If it was TN i would say, use 25mm Swa as the tails, armour earthed & also a seperate core for an earth. (and no rcd at the intake).
Q.1. Would this be correct & acceptable?
Q.2. If the tails were surface mounted in a TN installation i would just use standard tails 25mm (no rcd), would this be correct & acceptable?
However the installation is TT, therefore could the 30ma rcd be changed for 100ma s type? And could the tails be left? (The tails may not be deeper than 50mm in the building fabric.) Would the tails have been better installed in s.w.a with 100ma s type front end.
Is there a better way of doing this?
Sorry quite a few questions there for a friday morning. There are 3 of us having a debate over this. Maybe the chaps who installed it, should have had this debate :25:
Cheers