Industrial refit and we’ve screwed a bunch of metal clad 13’s onto walls which are corrugated metal sheet using self tappers. Just come to do dead tests and realised that r2 is about half the value of r1 and rn - the sheet is acting a conductor. Sup Bond the sheet or not? The same walls also have 32/3 socket outlets but they’re class 2 boxes, also the board is on the same walling. Structural is bonded back at the MET. So the low down is everything has an Earth path, just in an odd way!