russmossy
I have come across a situation where 6mm tails have been installed on the live side of the main switch of a distribution board. The supply to the DB is 35mm and I would guess on either 63 or 100amp fuses (unable to isolate at main panel to check). It appears that no spare ways were available so someone has tagged the cables in to feed a 4 pole, 32 amp breaker in an enclosure mounted on top of the DB. As usual the regs relating to this are clear as mud and our NIC guy will pick up his messages in about six months!
I think reading reg 434.2.1 in isolation, the situation conforms being that the tails are under the 3mtrs (only 1 mtr) and being run inside the DB, has reduced the fault risk to a minimum? However, I am not sure and would appreciate any advice.
On a similar note, I also have the situation where a 3 phase DB has been made into single phase by linking the incoming side of the main switch with 10mm cable from a 95mm incomer. Is that acceptable based on the criteria above?
I think reading reg 434.2.1 in isolation, the situation conforms being that the tails are under the 3mtrs (only 1 mtr) and being run inside the DB, has reduced the fault risk to a minimum? However, I am not sure and would appreciate any advice.
On a similar note, I also have the situation where a 3 phase DB has been made into single phase by linking the incoming side of the main switch with 10mm cable from a 95mm incomer. Is that acceptable based on the criteria above?