reference methods | on ElectriciansForums
Discuss reference methods in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
C
cagedanimal2010
hi guys,
whats the reference method, of t&e clipped direct to wooden joists above ceiling with insulation??
cheers guys!!
For a cable likely to be totally surrounded by thermal insulation over a length of more than 0.5 m, the current-carrying capacity is to be taken as the current-carrying capacity for that cable clipped direct to a surface and open (Reference Method C) multiplied by a derating factor (
[ElectriciansForums.net] reference methods
) for thermal insulation. In the absence of more precise information,
is to be given a value of 0.5.
Tabulated current-carrying capacities for various types of cable installed in a thermally insulating wall or above a thermally insulating ceiling - the cable being in contact with a thermally conductive surface on one side are given in Appendix 4 of BS 7671.
Regards
Dichroic
It'll either be method 100 or 101 depending on the thickness of the insulation, i.e less than 100mm = method 100, more than 100mm thick = 101.
Reply to reference methods in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
In the current book (18th, amendment 2) it is under regs 433.2 and 434.2 In most domestic situations the usual approach is the whole circuit is...
If cable is run through holes in joists, then turns through 90 degrees, clipped to the joist, then clipped to the brick wall as itvdrops to the...