Got a small job to put an extra socket in supplying tumble drier. If I label it as tumble drier only, can I omitt RCD protection? Is a FCU required aswell as the socket outlet?

Also I have a request to fit spots on a dimmer in bathroom. The dimmer is outside zone 2. Is it permitted inside a bathroom or will it have to be installed outside?
 
If the socket is behind the appliance and unlikely to be used for anything else then no rcd required.
If cable is buried in wall then rcd needed anyway.
Bathroom dimmer ok if outside zone 2.
so what if the cable was buried at a depth greater than 50mm...and/or was given additional protection by earthed metallic conduit....?....
 
Never thought of It like that...
Would that comply in the same way as MI and SWA then?
In terms of it being an earthed metallic sheath then, in my opinion, yes. With MI and SWA you have to connect the sheath to earth which is not required for FP as it is already connected to the CPC.
I feel that if you are trying to omit using an RCD for operational reasons FP is one of the easiest cables to use, when the cable is buried <50mm, for this purpose.
 
afraid i must disagree with the use of FP negating the need for an RCD. my reasoning is that the flimsy bacofoil cable covering does not comply " with the requirements of the regulations for a protective conductor........" ( reg. 522.6.6 (i))
 
I did think SWA and MI were the only earthed metallic sheaths i could really think of never seen FP used to avoid additional protection via RCD..........
Not so sure now, may have to check this out
 
afraid i must disagree with the use of FP negating the need for an RCD. my reasoning is that the flimsy bacofoil cable covering does not comply " with the requirements of the regulations for a protective conductor........" ( reg. 522.6.6 (i))

Agreed.
Put it this way , if the earth wires had been cut off at either end of the FP cable would you use the foil wrap as an earth conductor ?
Its there for heat resisting properties only.
 

Reply to Reg 411.3.3 in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hi everyone, If you are looking for reliable EV chargers, check out our top-rated selection at E2GO! ⚡ Please note that all EV Chargers and...
Replies
0
Views
106
  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
895
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K

Similar threads

  • Question
When I was at college doing the 2361 back in the 1980's I still recall to this day the instructor (Mr Wood) saying "Lads I do not want you to...
Replies
10
Views
678
  • Question
ok cheers for the help lads
Replies
7
Views
816

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top