Looking at some work for a lady who has recently had a new fitted kitchen.
She was concerned about some bits so I had a quick look and found a 3.5KW oven on 1.5mm T&E to a 13A plug top.
Can anyone tell me the reg numbers for loads over 3KW needing thier own circuit, not using T&E into a plug top and for following manufacturers instuctions (and any others that may be wrong).
Thank you.
 
Cooking loads over 2kW should not be supplied from a ring according to a note in appendix 15, T&E is advised in the ISITEE guidelines as being unsuitable for a use in a plug becauce the cable is not designed for frequent movement. 134.1.1 and 510.3 "shall take account of manufacturers instructions".
Cable is suitable for the load.
 
Not to mention twin and earth into a plug top is proper badgers....

I have seen an entire brand new block of flats where all the fitted ovens were installed by the kitchen company on 1mm twin and earth via a plug top into a 13a socket directly behind the oven (no isolation switch) fed from a 40a radial in the board

Nice work fellas
 
Cooking loads over 2kW should not be supplied from a ring according to a note in appendix 15, T&E is advised in the ISITEE guidelines as being unsuitable for a use in a plug becauce the cable is not designed for frequent movement. 134.1.1 and 510.3 "shall take account of manufacturers instructions".
Cable is suitable for the load.
Thank you
 
Not to mention twin and earth into a plug top is proper badgers....

I have seen an entire brand new block of flats where all the fitted ovens were installed by the kitchen company on 1mm twin and earth via a plug top into a 13a socket directly behind the oven (no isolation switch) fed from a 40a radial in the board

Nice work fellas

They are plugs NOT plug tops which are the covers for the plugs.
 

Reply to Regs book at office in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
514
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
2K

Similar threads

  • Question
Its important to remember that a plug top fuse is just a rewireable fuse that's convenient to change and shouldn't be confused with a HRC fuse...
2
Replies
15
Views
1K
Thanks all for your comments, advice and suggestions. The following is probably pretty boring for most, and is simply a summary of how the job...
Replies
8
Views
923

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top