I haven't got the reports in front of me but from memory they are 3x2.5's in a 16 breaker so no danger
A single or double socket taken off an RFC MCB at the CU is perfectly acceptable in 2.5mm, as it is no different than a spur from any other point in the Ring. Only 1 allowed, mind.
So if you decide to run another final circuit, ie a run of Radial sockets or lights how does dipping into a used way comply with this reg ? I'm not saying your necessarily wrong but it seems clear cut ?
I will need to have a chat with them I like the analogy of the circuit being cut in two inches from the board good that is, I don't think nikky said it was dangerous just a C2, in 314.4 it states..
Where an installation comprises more than one final circuit, each final circuit shall be connected to a separate way in the distribution board.The wiring of each final circuit shall be electrically separate from that of every other final circuit, so as to prevent indirect energizing of a final circuit intended to be isolated.
So if you decide to run another final circuit, ie a run of Radial sockets or lights how does dipping into a used way comply with this reg ? I'm not saying your necessarily wrong but it seems clear cut ?
I think you are missing a point here, it is not another final circuit, it becomes a part of the same final circuit, see Johnboys post about definitions in part 2.
I am struggling with this thread........
Why am I struggling?
Well, if you are a member of an authorizing body, such as the NICEIC then you are bound by their regulations to follow their rules.
So there is not much you can do. If your assessor tells you that you cannot use SWA as an earthing conductor, or you have to use a taped up crimped ring connection on MPBC, or having 3 * 2.5mm2 conductors in a 32A MCB where two of them form a RFC is potentially dangerous, then you are obliged to follow their rules. A departure from their rules will initiate disciplinary procedures.
I'm not a member of this 'bend down and kiss my ring, on my finger' club so their rules don't apply to me or to anyone else who is not a member.
Just a note to think about:
What do you think might happen to a socket outlet supplied via 2.5mm2 cable protected by a B32A MCB ?
Yes, BUT, I think the OP is referring to an old CU where there are more circuits than fuses
If I can put it another way.
Say we did something really daft (for arguments sake), say we had 4 downstairs lighting points, and each had it's own supply cable, and we terminated all 4 conductors on a 6A fuse, is this any different than using the loop in loop out or 'Spider JB' method electrically speaking ?, and would it warrant a C2 ?