What do you think might happen to a socket outlet supplied via 2.5mm2 cable protected by a B32A MCB ?
The point of only having 1 single or double socket from a 32A MCB as a spur is that the plugtop fuses will be essentially protecting the cable. Granted, you could have 2 lots of 13A connected meaning 26A (very close to the 27A limit of Ref method C), but the point is that the cable IS protected.
You could also do 150mph down the high street and something bad would probably happen, but it's unlikely you would....