So I’m currently studying Ze and pfc etc kind of understanding it.
main question really is about the relationship between them both I understand that the lower the Ze the higher the fault current but why is this? Is it just simply to do with ohms law? And I’m just over thinking and confusing myself

Any responses would be appreciated
 
I think it buried in the Multiverse with Jean Luc Picard. ? If anyone is confused it's a joke.

I find my sense of humour is directly proportional to the amount of wine I have drunk, I'm a giggler not a fighter. ?
 
The less the resistance the easier a current is able to flow. The better the flow the bigger the bang. Of course practically a higher resistance can lead to a current flow that is too low to cause the OCPD to operate within the times required by BS7671. So the measuring of Ze/Zs has a number of ramifications to it both ways, i.e. is it too high or too low, each has their own problems.
 
The IET's "Electrical Installation Design Guide" has some examples of the slightly more tricky cases on pages 76-81

Great little book, BTW - I can strongly recommend that anyone who wants to understand more should get a copy.

Also Paul Cook's Commentary on IET Wiring Regulations. Unfortunately the most recent one is for the 17th Edition (dunno what's going on there), but as the laws of physics dinnae change, it's still a useful book. Maybe, given it's now out of date, try to get a s/h copy on eBay - they are around.

 
Here's an interesting exercise for y'all. Look up the amount of energy in a stick of dynamite, and compare it to how long a supply cable fault upstream of a cutout has to last to release the same amount.
Or watch the video:

Admittedly that is a lot more PFC that a domestic system will see, but still impressive what it does.
 

Reply to Relationship ze and pfc in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
771
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
978

Similar threads

FFS - popped it apart, found the same issue and thought I'd update... You guys were already there!
2
Replies
21
Views
2K
  • Question
Yes I touched on diverted neutrals when I went over guidance note 3 the first time but I’m doing a second round and going between all books whilst...
Replies
9
Views
631

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top