Avidude

hi i am looking to take my napit exam.
i want to replace a garage consumer unit,
i have looked and found that it is using the swa as the earth (2 core swa)
what can i do?
can i use the swa as the earth for the new consumer unit?
i don't want to have to use a TT system.
thanks for any input
avidude
 
what size SWA. and can you get a Ze reading from the garage end? might be better to make sure the SWA armour is earthed at the house end only, then TT the garage. That way you will only be assessed on your work in the garage. be sure to RCD/RCBO both circuits.
 
Last edited:
Hello
the swa is only 2.5 2 core,
i fond that the swa was not even connected at the board (So there was no earth)
i have never worked with tt system before.
where can i find out where to buy and how to use earth rods?
 
any wholesaler will sell you a rod and clamp for about ÂŁ10, just knock the rod into the ground fit the clamp on the end and tie your earth to it.

alternatively run a seperate earth from the met to the garage (exporting of earths may or may not be an issue)
 
Last edited by a moderator:
As it's a TN-S system, using the armour as the CPC is totally acceptable.

Make the SWA a 20A radial circuit from the house CU and install a garage CU at the garage end. Most likely it will come with a 40A 30mA RCD, & 1 x 16A & 1 x 6A MCB's.

Make sure the SWA is glanded correctly at both ends and there wont be an issue.
 
as both previous posts. earth rod,(missing drains etc) drill concrete floor, whack it in, no aggro with exsported earth, connection in proper box and flagged with safety earth blah, blah tag., 10mm G/Y in pvc tube to CU. nice job.
 
As it's a TN-S system, using the armour as the CPC is totally acceptable.

Make the SWA a 20A radial circuit from the house CU and install a garage CU at the garage end. Most likely it will come with a 40A 30mA RCD, & 1 x 16A & 1 x 6A MCB's.

Make sure the SWA is glanded correctly at both ends and there wont be an issue.

This is what i'd be doing too.
 

Reply to replaceing consumer unit in shed (with no earth) in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
352
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
901
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

I hate it when a shed is TTd, why can they not be extended from the tn system? popcorn ready
Replies
7
Views
674
I opened up the CU again and the round junction box above and what I found was the blue and brown wires coming in from the wall just above the 15a...
2 3
Replies
33
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top