Another hob wiring question sorry,

I am replacing my oven and hob and the oven connections was fine, 6mm from new consumer unit on a 32a RCBO split to oven and hob.
the new hob is 6.2kw, old hob is 6kw the new one will not take the 6mm cable that was connected to the previous hob and the instructions say use 2.5mm cable.

I would like to use 4mm cable minimum due to the 32a RCBO what cable do you recommend if this is ok?
The links between the connectors are still in place.

I have attached pics.

Thanks
[ElectriciansForums.net] Replacement Hob Wire size

[ElectriciansForums.net] Replacement Hob Wire size
[ElectriciansForums.net] Replacement Hob Wire size
 
2.5mm seems small, though with diversity it would be 10 + 0.4 * (27.4 - 10) = 17A so usually OK.

I certainly would look at 4mm, or at least a 2.5mm that is rated for 90C operation such as the LSZH version of T&E. For example, here it is sold by the metre (both 2.5mm and 4mm below):
Also high temperature flexible cable:
 
as said 2.5 flex of a heat resisting type is adequate but if you're not pleased about it, if you look hard you'll find 5x2.5 so you can double up for 2x L, 2x N, leave the links in. I carry a bit specifically for hobs as the stupid terminal setups are often made for continental polyphase installs.
 

Reply to Replacement Hob Wire size in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
380
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
957
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

I believe the 6mm and 40A MCB debate is a little contentious at times. It depends on the installation method, being pretty close to the tabulated...
Replies
3
Views
406
I've put a 2 way unit inside kitchen cupboards before now if we were re-using the original cooker supply but the customer wanted 2 x 16A ovens. I...
Replies
8
Views
438

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top