Joined
Feb 7, 2009
Messages
360
Reaction score
16
Location
.
Just done 80% rewire in house where 12m of 6mm t/e shower cable replaced with 10mm t/e to allow upgrade of shower which has already been done prior.
However, due to other extensive work in house it was simple to replace all cable from consumer unit to shower pull switch but the cable from pull switch to shower unit is approx 1m down a newly tiled stud wall and is still coppper 6mm t/e.
Question is - will that 1m of 6mm t/e still mean shower can only be upto 7.6kw if wall insulated and 8.7kw if not insulated.
 
In theory the entire circuit should be rated for the 6mm section, on the other hand the regs have a get-out clause for cable calcs along the lines of "dependent on the electricians judgement and experience", so if your load is only slightly over what the 6mm can "officially" take, you might "get away with it". Judgement call on your (or another electrician's) part!
 
can be fitted with the aid of.............




[ElectriciansForums.net] Replacement shower cable
 
I've used a Bosch PMF180E with the diamond blade to remove the grout between the tiles, pulled them off and replace with new after needing to do a similar job. But I had spare matching tiles to hand. Might be an option if the 6mm really won't do.
 

Reply to Replacement shower cable in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
60
  • Sticky
  • Article
Wicked I've just actually looked through it and it's very smart. Some good stuff in it. There's a tile association company that do a magazine...
Replies
2
Views
389
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
347

Similar threads

  • Question
Better off with the click prw213 as it has twin screw termination.
Replies
9
Views
926
  • Question
One thing you may find is that it will most probably be a 6mm cable and to get two of them in to a terminal may prove to be a stumbling block if...
Replies
3
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top