mikeshums

DIY
Joined
Dec 20, 2023
Messages
2
Reaction score
4
Location
New Hampshire
I have a detached garage with a 60 AMP subpanel which has lost power. I traced the failure to the wire running under the walkway via conduit (about 15 ft) and can see it fried on the detached garage side. I suspect age, critters and or water got to it and shorted it out.

If I replace the wire from the sub-panel back across the walkway what is the requirement for creating a junction at the point it leaves from the main house? I'm hoping that it's not required to do a single intact new run all the way back to the main service box in the house. thanks.
 
I would suggest an insulation test on the cable you wish to re-use back to the main board to verify its still in good condition, this will probably need the use of a MFT which all electricians will have.
 
So this was resolved. I used a line tester to see if I had power across the breaker on the main box in the house. Breaker tested fine. Then I checked power along the line and found that I had power exiting the house but no power entering the detached garage. I pulled the cover off the conduit box and saw it was burnt through. Mice (2 carcasses :) ) Junction box on the house side, new wire to the sub-panel and we're in business.
 

Reply to Replacing run to detached garage sub panel. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

  • Question
Yes you will need to install # 4 wiring times 4 for your 2 hots, 1 neutral and 1 equipment ground. As for keeping the grounds and neutrals...
Replies
3
Views
1K
  • Question
You'd end up buying a 100 amp panel anyways, because the scale they're manufactured end up cheaper than non-typical equipment, and often come with...
Replies
3
Views
1K
Honestly look at the double pole 4 wire receptacle on the generator because I think that it just has a 30 amp circuit. Anyway # 6 copper wire is...
Replies
8
Views
1K
  • Question
There is nothing inherently wrong with this part of the layout. There is another option that you may want to consider. Those supply conductors...
Replies
3
Views
1K
I want to verify if the breaker size is correct for the service going into my detached garage. I have 6 AWG cable going from my main panel in my...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks