We have a room in the house that was the kitchen. That has been relocated to a different area, so the old kitchen has been sold off and the room will be a bathroom. I’ve studded out the room and lined with cementitious board ready for tiling. All first fix plumbing is done. All sockets are obviously redundant. So they have been removed and the ring made good using wago junction boxes. The ring will feed a laundry / utility.

There is also a 5mm cooker radial. This goes to a point where there was presumably an oven in the past. The radial was extended by some superstar using 2.5mm T&E right round the room (about 9m) to a cooker switch connected to a range cooker. Was hidden behind units so no one knew. Short connection to old range from switch was in 6mm cable. I’ve ripped out the extension bodge.

Question

Pretty sure this is OK but would like confirmation or contradiction please. Radial can easily be fed to a useful double sockets or pair of double sockets in an adjacent room (which will be a bedroom) through the stud (no evidence in new bathroom). Total radial length is roughly 12m. Assuming we change the MCB or fit an RCBO of suitable size in the CU, there is presumably no reason why I can’t use the cable for a couple of sockets and possibly an LED light spur on a 3 amp switched spur socket? The fact that the cable is way over spec for this kind of use is not a problem on the principle that too big is better than too small? Or am I being dim witted?
 
Thanks. Current 2018 Hager board has 2 RCDs and 8 MCBs each side (not all used). My intention is to ditch this in due course (later this year or next year) and replace with a full RCBO CU with surge protection and possibly AFDD.
 
One thing you may find is that it will most probably be a 6mm cable and to get two of them in to a terminal may prove to be a stumbling block if you intend to run the same size cable all the way ! It may be just as easy to replace the short run all the way ! Just a thought.
 

Reply to Repurposing a cooker radial? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
430
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
I have to agree with Baldelectrician on almost everything he says except one ! I wouldn’t be walking away I’d be running lol. Definitely if your...
Replies
13
Views
2K
  • Question
Why aren't you asking them?
Replies
5
Views
866

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top