Normally I fit local isolators adjacent to 3 phase motors to allow for maintenance. I have been informed that as my main control panel is within 8 meters at most from any one motor on the plant I can install a lockable emergency stop push button to kill the control circuit and use this as a suitable replacement. What are your thoughts? Is there a regulation for a requirement of local isolators as I cannot find one specifically stating that it's required.
 
Locking the control does not under any circumstances equate to isolation. Locking the panel isolator does.

Something I did on a panel feeding over 100 drives. I took the outgoing from the panel isolator through various isolators dotted around the plant then back to the panel.
 
No where in the regs does it say that motors should have LOCAL isolation. I used to think it did....

Section 132.15.2 Every fixed electrical motor shall be provided with an efficient means of switching off, readily accessible, easily operated and so placed as to prevent danger.
 
Personally, i don't give a damn what it say's in BS7671, or any other standard, ...local isolation is always provided to any motor driven machinery/equipment!! And local will mean local too, not several metres away or round a corner out of sight!!

I agree with Tony too, in that locking a control circuit, does not equate to the safe isolation of power...
 
If there is a motor drive, then it will need to be worked on at one time or another. Therefore local isolation (preferably locking) be it for maintenance purposes, emg isolation etc,etc, should always be required...
 
As you have mentioned on post 7, you don't give a bamn what the regs say about this, but I have to say again that no 'local' isolation is required. It is nice but not compulsory.
 
As you have mentioned on post 7, you don't give a bamn what the regs say about this, but I have to say again that no 'local' isolation is required. It is nice but not compulsory.

Yep and another reason why i take little notice of BS 7671 when it comes to full on commercial/industrial installations. ...And it's nothing to do with it being nice to have!! lol!!
 

Reply to Requirement of local isolators for 3 phase motors on plant in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
299
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
807
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
848

Similar threads

I got this all wired in and working thanks to the help from James, absolutely top man. Do have a small issue with current imbalance atm, L3...
Replies
10
Views
2K
I can imagine it just disappearing (loudly) under short circuit conditions, then the resulting blast/plasma etc. casing the busbars to flash over...
Replies
13
Views
695

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top