You need to look further than BS7671 as this may be irrelevant to motor controls like this remember check the exclusions from scope.

In the UK there will be statute law to consider, forget BS7671.
 
I know that to add this is very late but just in case someone is trying to find out what to do then........LOOKING AT ELECTRICAL REGULATIONS IS THE WRONG PLACE; LOOK AT HEALTH AND SAFETY.
Quote "Where maintenance requires that normal guarding is removed, or access is required inside existing guarding, then additional measures are needed to prevent danger from the mechanical, electrical and other hazards"....... "The basic rules, however, are that there should be isolation from the power source (usually, but not exclusively, electrical energy), the isolator should be locked in position (for example by a padlock), and a sign should be used to indicate that maintenance work is in progress. Isolation requires use of devices that are specifically designed for this purpose; not devices such as key-lockable emergency stops or other types of switches that may be fitted to the machine".
One point that has not been mentioned is size /rating of the isolators. If the rating is less than the contacts can safely break when some one switches the motor on or off whilst on full load or full starting current you will need to have an isolator that breaks the control circuit before breaking the power circuit (early brake late make contacts) and the opposite for when you switch the isolator back on. This also means you have to run wiring for the control circuit to the isolator as well as the power cable. And no just running the control circuit through the isolator is not sufficient.
 

Reply to Requirement of local isolators for 3 phase motors on plant in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
298
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
807
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
848

Similar threads

I got this all wired in and working thanks to the help from James, absolutely top man. Do have a small issue with current imbalance atm, L3...
Replies
10
Views
2K
I can imagine it just disappearing (loudly) under short circuit conditions, then the resulting blast/plasma etc. casing the busbars to flash over...
Replies
13
Views
695

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top