I have a reading of 5ohms when checking resistance between neutral and earth, it's a TNCS installation. Is this a little low? I checked this after finding spurious readings on a central heating boiler, whilst doing preliminary electrical checks. Any help, anyone
What resistance would be expected? I know the neutral and earth join after the circuit board, back to the sub station, so resistance would be reasonably low, but this is quite a large industrial premises
thought you were measuring at DB. if you're measuring a a point on a circuit, the reading will depend on the cable from the DB. even so you should find that Rn+R2 is equal to R1+R2.
Dont get what you are trying to achieve....It's a TNCS so you would expect a low resistance between N-E anywhere on the system with N and E still connected...and if you are IR testing it would not be possible to register a reading of 5 ohms.
Reply to resistance reading between neutral and earth in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
I was at the other end of the results spectrum today. As I was driving home I had a call from my "Mrs Richards from Fawlty Towers" lady, very deaf...
I may have been mistaken regarding TT I will look into that, thank you for the valued reply, but in general I stick to my post, a good topic for...