Hi folks.
I'm getting ready for some upcoming exams and I find myself tripping up over resistivity equations. I've been working through example questions, but this one confuses me.

Example:
Find the CSA of a single copper cable 500 metres long, which carries a current of 2.5A, and has voltage drop of 3.58V, resistivity of copper being 1.72x10(-8) ohm/m.

any help would be great!
Thanks :)

Gary
 
IMG_3083.JPG
 
You are normally given the CSA in a question, or as you say you could not work out the answer. Ok sorry just seen its a reverse question. Silly me. So reverse engineer the figures.
 
Last edited by a moderator:
use ohms law to work out Ohms. V/I

I then used the formula and put a Value for CSA in that is not known yet.

I will, give you a clue, It is less than 10mm2.

I expect there is any easier way though.
 
You are given the formula R = rho x l/csa.

One has to re-arrange this formula to put your unknown, the csa = ...

The trick is to do the same thing to both sides of the equality (=).

So, csa x R = csa x rho x l/csa which can be re-arranged on the right hand side to:

rho x l x csa/csa. But csa/csa = 1.

One can now write csa x R = rho x l

Use the same trick again but this time divide both sides by R to arrive at csa = ...

I leave you to finish it off.
 
I don't know what that page is an extract from but it trips over this a couple of times. The resistance of a one-metre cube of copper isn't any number of Ω⋅m, then when they do mean Ω⋅m they call it ohms per metre. Doesn't anybody check this stuff before printing (could that be another 'replica' like the dodgy BS7671s?). People don't make these mistakes in daily life ('I'll have half a minute of potatoes and two dozen per-egg-squared please') so it's a bit poor that they crop up so often in supposedly technical stuff.

Marconi gives the right strategy - rearrange the formulas you have, and/or substitute into one another until you have your unknown in terms of your known values. You can also substitute V=IR into it so that you have only one equation to solve, that takes in all the data given in the question and spits out the CSA. But, if you find that too abstract, you can calculate in stages. i.e. you know the voltage drop and current, so you can calculate the resistance, and once you know that you can use it and the resistivity and length to calculate the CSA. Sometimes knowing the solution of the intermediate steps is helpful because it can show up mistakes, or feed other parts of a multi-part question.
 
I find using the diagonal method the easiest.

r = pl
-----
a

So in this case you want to find a (csa)

The pl would move diagonally across to become:

r = a
----
pl



If you wanted l then you would use the same technique:

r = pl
-----
a


Move p below r

r = l
---- ----
p a



Now a move across diagonally to r leaving l on its own

ra = l
-----
p



Hope this posts keeping the format as its done on my mobile
 
Last edited:
Quite a long time since I did this so i could be way off but are you sure it's not

a= pl/r

If I were to break It down..

Step 1. (Move "a" over the equals sign to the top of the equation) so you end up with.

ra=pl

Step 2 (move "r" over the equals sign so it ends up at the bottom of the equation e.g. divide instead of multiply)

a=pl/r
 
Last edited:
transposition of formulae is easy if you just bear in mind that you can do anything like add, subtract,multiply, or divide .just ensure that wtatever you do, do it to both sides of the equation. e.g. if you divide the right side by x, then divide the left side by x. both are then still equal.
 
@Gary. Try to visualize it this way if it helps:
A 500M length of 1M^2 cable (wow that's a big fat one) would be 500*1.72e-8 = 8.6e-6 ohms.
Your 500M cable is 1.43 ohms. Hence as a fraction of 1M^2, the CSA is simply one over the other. = 8.6e-6/1.43. - And that's in square metres.
Since there are 1000*1000 square millimetres in a square metre, multiply the answer by 1000000. QED
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Peterborough
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Trainee Electrician

Thread Information

Title
Resistivity equations
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
17
Unsolved
--

Thread Tags

Advert

Thread statistics

Created
Gary Tollison,
Last reply from
COOKIET123,
Replies
17
Views
11,747

Advert

Back
Top