Trainee
If I place say an 80 Ω resistor across L-N, would that generate a load of approx 2.8A.

I’m looking to create an artificial load of a socket circuit so I can locate the current at the DB using a clamp meter.

Used to use plug in 3kW heaters but not an option anymore, also definitely not able to isolate the power to test.

Thanks in advanced!! :)
 
If you want to put a load on a circuit... you can still buy 2kW fan heaters... what's wrong with them? Or a kettle?

Or as @grumpyjohn01 suggests, a circuit locator? Although it's not a precise science as the signal injected into the circuit will appear on others and at the board it can be a bit hit and miss.
 
If you want to put a load on a circuit... you can still buy 2kW fan heaters... what's wrong with them? Or a kettle?

Or as @grumpyjohn01 suggests, a circuit locator? Although it's not a precise science as the signal injected into the circuit will appear on others and at the board it can be a bit hit and miss.
Agreed, not an exact science but if you persist you can usually track the right one down. If you don't know which circuit a socket is on you may also not know if there are existing loads as well so in that case putting a known load on may not be an exact science either!
 
I’m going to get one of those for that stately home testing job coming up.
I've got the 'socket & see' one ,originally acquired for a hospital testing job. As Sparkychick says they are not an exact science but the longer you scan for they reckon to filter out the weaker signals and eventually you are left with the right one. In my experience with a few other clues and your 'supersparky senses' you can usually get there in the end. Not so much of a problem if you can isolate to confirm but a bit more nerve-wracking in a medical environment..!
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Gurnatronics

Trainee
-
Joined
Location
Derby
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Electrical Engineer (Qualified)

Thread Information

Title
Resistor across L-N in an adapter box. Possible or asking for trouble?
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
21
Unsolved
--

Advert

Thread statistics

Created
Gurnatronics,
Last reply from
pc1966,
Replies
21
Views
2,127

Advert

Back
Top