I was called out yesterday to a house to have a look at a wall mounted heater in a bedroom that had stopped working. Had a quick look, and noticed that the heater was controlled by a 20A DP switch. No FCU. In the CU, it was on a 32A MCB. Upon further investigation, I found that there were two 3kw heaters on this circuit. Basically, the 10mm^2 shower circuit had been repurposed to supply these heaters. Nothing unusual about that but the way it was done was a bit rough (in my view). The 10mm^2 cable was terminated into a cooker outlet plate, then 2 x 2.5mm^2 cables came out of this plate, immediately into 2 x unswitched FCUs, then onto the heaters which had local 20A DP switches. I fixed her problem by simply replacing a fuse. But it got me thinking how I would have done this job and if the current situation is acceptable. The connections in the cooker outlet were sound, no cable can be overloaded, so at the time I couldn't immediately fault it. I suppose the cooker outlet wasn't designed for the purpose it is being used for. If I were doing this I would probably just stick a small 2 way CU with 2x 16A MCBs in it on the end of the 10mm^2, or find a more suitable way of joining the cables.
Any thoughts?
 
The 2 x 16A MCBs would cover it. But I guess the question is - is it necessary? The 2.5 should be able to meet fault disconnection for 32A MCB ok (?) so it's overload current that remains. This was covered by the 13A FCUs used, but from immersions I've found many of these don't like 3kW loads. Does reg 433.3.1 (ii) help us? The heater draws 12.5A and it's hard to see (to me anyway :) ) how one could draw a current that would overload the 2.5 ?
 

Reply to Reused shower cable (for heaters) in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
961
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

I've put a 2 way unit inside kitchen cupboards before now if we were re-using the original cooker supply but the customer wanted 2 x 16A ovens. I...
Replies
8
Views
440
Being pedantic, the Crabtree 50A cooker switch is a 4500/1, which has 'cooker' printed on it. For a shower, you require the 4500, which is the...
Replies
3
Views
340

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top