reverse polarity on appliance socket | on ElectriciansForums

Discuss reverse polarity on appliance socket in the UK Electrical Forum area at ElectriciansForums.net

Joined
Dec 24, 2016
Messages
404
Reaction score
82
Location
london
Carried out an eicr and noticed x2 double sockets have reverse polarity that supply a frying machine at high level.
After correcting the reverse polarity on the two sockets i plugged the fryer back in and the circuit MCB tripped out and the appliance popped.

I am unable to open the fryer up as its fixed into the unit.

I cant seem to work out why the original appliances required the sockets to have incorrect polarity at the socket, and after correcting the reverse polarity the appliance tripped the fuse.

I checked the newly configured polarity and the sockets were correctly wired wheres before the L-N had been reversed.
 
Last edited:
Carried out an eicr and noticed x2 double sockets have reverse polarity that supply a frying machine at high level.
After correcting the reverse polarity on the two sockets i plugged the fryer back in and the circuit tripped out and the appliance popped.

I cant seem to work out why the original appliances required the sockets to have incorrect polarity at the socket, and after correcting the reverse polarity the appliance tripped the fuse.

I checked the newly configured polarity and the sockets were correctly wired wheres before the L-N had been reversed.
What tripped CB,RCBO or RCD what instrument did you use to confirm correct polarity? looks like you need to carry out some more test on the circuit supplying the 2 twin sockets
 
Without the fryer plugged in the MCB stays on, i checked the plug top and it was fine.
Fault on the fryer then, diagnosing from afar. As the job was an EICR thats, an inspection of the fixed wiring, which you have found and rectified a fault, your client needs to get the fryer tested under ISITEE the new way of saying PATesting, in my opinion.
 

Reply to reverse polarity on appliance socket in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
959
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
Im not as clever as you guys. I would be doing what somw others have said, I would be leaving certain items switched off for a period of time...
2
Replies
19
Views
2K
When I was on the electric board We had a pair of pillocks connect a housing estate to a very large genset, the n lead was in two parts and not...
2
Replies
28
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top