Dear all professional electricians
This is the report we were sent by our seller. Does this report look okay, especially the readings. If anything is missing I would be grateful if you could point it out.
Screenshot 2025-01-13 at 23.34.13.png

Thanks
Screenshot 2025-01-13 at 23.34.43.png
Screenshot 2025-01-13 at 23.35.37.png
Screenshot 2025-01-13 at 23.35.50.png
 
Couple of things stand out.

61009 is not a suitable main protective device type.

Mainswitch rating is stated as 100V as well as 100A. Should be 230V

Every measured Zs is exactly the same. (0.68 ohms) This should be different for every circuit….

His C3 coding at the beginning mentions putting surge protection in, but his circuit schedule has a surge device ticked as being present.


Looks like a rush job to me….

Do you know how long they were in the property for?
 
Dear all professional electricians
This is the report we were sent by our seller. Does this report look okay, especially the readings. If anything is missing I would be grateful if you could point it out.

This report is worthless as per the replies given above. I am suspecting this is a copy and paste job with bits left in from a previous report. ie Earth Mat for details of the Electrode when it is already stated it is TN-C-S and earthing is supplied by the distributer and Earth Electrode is N/A.

As other have said DC for the supply? 100V main Switch and it is apparently only 1 pole.

As stated above readings all the same on different circuits?

Could go on.
 
IR test voltage is quoted as 200 but probably should be 250.
No RCBO readings or types, assuming they are 61009.
No ring final readings.
I suspect the protective devices are 6ka not 10ka.
Has confirmed phase sequence when it is probably single phase.
 
The list of mistakes is getting longer.

I did notice the IR was “200” on some and “>200” on others, which is more likely. Pointed out by westward above


Also, out of interest, was the overall outcome marked as “SATISFACTORY”? Which is what a single C3 would bring about?


Without being on site ourselves, we can’t say how good the installation actually is, but it’s a sure thing that the report itself is a load of rubbish.
 
Couple of things stand out.

61009 is not a suitable main protective device type.

Mainswitch rating is stated as 100V as well as 100A. Should be 230V

Every measured Zs is exactly the same. (0.68 ohms) This should be different for every circuit….

His C3 coding at the beginning mentions putting surge protection in, but his circuit schedule has a surge device ticked as being present.


Looks like a rush job to me….

Do you know how long they were in the property for?
Thank you for your inputs.
SPD: 61009 is not suitable. Should it be BS60947?
Mainwitch current rating: should it be 100 A & voltage raring should it be 230 V?

Measured Zs: Is this under schedule of circuit & test results? There are different Z values there. About SPD, thank you for that. I didn't even realise it.

This electrician is NICEIC registered. Im not sure how long was the inspection.

We are very frustrated, since this is the second electrician called for inspection. The first one was NAPIT registered & apparently there were glaring faults in that report too. We have a disabled wheelchair bound child at home & we need peace of mind that electrics are safe in the house. But the certified, registered electricians are now coming up with reports as work of art, very subjective to interpretation. The earlier electrician produced the report as follows


Screenshot 2025-01-14 at 18.32.13.png
 
This report is worthless as per the replies given above. I am suspecting this is a copy and paste job with bits left in from a previous report. ie Earth Mat for details of the Electrode when it is already stated it is TN-C-S and earthing is supplied by the distributer and Earth Electrode is N/A.

As other have said DC for the supply? 100V main Switch and it is apparently only 1 pole.

As stated above readings all the same on different circuits?

Could go on.
I am feeling so let down.

This is the second guy doing report. Both registered.

How do I find a competent guy?
 
IR test voltage is quoted as 200 but probably should be 250.
No RCBO readings or types, assuming they are 61009.
No ring final readings.
I suspect the protective devices are 6ka not 10ka.
Has confirmed phase sequence when it is probably single phase.

According to the schedule circuit 3 is spare with a missing cover, Code 2?


Thank you for your inputs. This is the second report commissioned. To be honest I'm still trying to make sense of what you all have written, grateful for the feedback. Though I am frustrated that certified electricians can be so incompetent. This is the CU pic, not sure if this can help make some sense of the report.

Also, possible C2, that's concerning! :-(

Consumer Board 20241109_134346.jpg
 
Last edited:
The list of mistakes is getting longer.

I did notice the IR was “200” on some and “>200” on others, which is more likely. Pointed out by westward above


Also, out of interest, was the overall outcome marked as “SATISFACTORY”? Which is what a single C3 would bring about?


Without being on site ourselves, we can’t say how good the installation actually is, but it’s a sure thing that the report itself is a load of rubbish.
Yes, this report says 'Satisfactory'.
Incidentally the earlier report done in Dec 2024, also said 'Satisfactory' though the numbers/readings in the two reports are wildly different. The electrics are 15-16 years old, house built in 2009-10

Westward surmises that it could be C2 since according to the schedule circuit 3 is spare with a missing cover. That would mean potentially dangerous.

1736881771239.png
 

Reply to Review of EICR in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
729
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
972

Similar threads

I usually put something like this To assess compliance with BS7671 for continued safe operation (5 year periodical inspection)
Replies
8
Views
572
Thanks for the reply littlespark. Yes the works have been carried out. Surely it is fraudulent because basically the document is Not...
Replies
2
Views
928

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top