No the primary protective device details are not correct on that second report you have attached.SPD: 61009 is not suitable. Should it be BS60947
What is your general location within England?
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Review of EICR in the UK Electrical Forum area at ElectriciansForums.net
No the primary protective device details are not correct on that second report you have attached.SPD: 61009 is not suitable. Should it be BS60947
Im based in Kent.No the primary protective device details are not correct on that second report you have attached.
What is your general location within England?
I do feel for you.Im based in Kent.
I have attached two reports, latest one done in Jan 2025 (NICEIC registered) in my original post & in replies another report done in Dec 2024 (NAPIT registered). Seems both are terribly wrong.
Sadly all too common. Once you see such basic errors there is nothing in the rest of the report you can trust.Im based in Kent.
I have attached two reports, latest one done in Jan 2025 (NICEIC registered) in my original post & in replies another report done in Dec 2024 (NAPIT registered). Seems both are terribly wrong.
These reports have eroded trust in registered bodies & tradespeople.The second one you put up (the earlier date) isn’t much better I’m afraid.
How they can get things so wrong is beyond any of us
Unfortunately, to the layman, these lists of BS numbers, measurements, strange combinations of letters and numbers are all very confusing.
That should read that '3' is a spare way , ie, that point in the consumer unit is not in use.Could you please look at this & comment? Is the Spare cover missing for 3?
There's an awful lot of n/a on the report .2.5 live conductor size and 2.5 cpc sizeDear all professional electricians
This is the report we were sent by our seller. Does this report look okay, especially the readings. If anything is missing I would be grateful if you could point it out.
View attachment 119384
ThanksView attachment 119383View attachment 119382View attachment 119381
It may have been mentioned previously on post because there are so many bizzare entries on sheet but there are no results for your socket ring continuity. 2.5 cpc for sockets assuming it's twin and earth ?,10ka breaking capacity ?no rcd trip time ,61009 for rcd?the first 2 circuits arnt even rcbos .type of rcd ?rip it up and start again .I've never seen a circuit chart like that before ,if your going to cheat and just take the cover off the board at least make it look believable. I no way am I endorsing drive by testing just seems bizzare almost like the apps went crazy .I was told by a select advisor (there in Scotland) that some electrical bodies are actually using there own staff to check some of these eicrs in London as they suspected as much as 50 percent were completely false.sparkies get copies of previous report and change it slightly without even taking there tester out its caseDear all professional electricians
This is the report we were sent by our seller. Does this report look okay, especially the readings. If anything is missing I would be grateful if you could point it out.
View attachment 119384
ThanksView attachment 119383View attachment 119382View attachment 119381
Dear all professional electricians
This is the report we were sent by our seller. Does this report look okay, especially the readings. If anything is missing I would be grateful if you could point it out.
View attachment 119384
ThanksView attachment 119383View attachment 119382View attachment 119381
Thank you Tom for explaining it so well.That should read that '3' is a spare way , ie, that point in the consumer unit is not in use.
If no circuit breaker at that position there would be an opening. Any such unused way should therefore have a [suitable] protective 'barrier' in place to prevent a person coming into contact with live parts that lay within the board.
From what I can see the opening is covered with a barrier that would not appear to be easily dislodged and suitable for purpose. The same form of barrier can be seen at other positions in the consumer unit and such has not be raised as an issue.
Would he have replaced the barrier at the time of the inspection? If there was such an opening it should be addressed and not left unchecked.
A length of tape over an opening would not be a suitable 'cover', what you have there would appear to be a barrier intended to be used for the purpose.
I cannot claim that I understood everything you wrote.There's an awful lot of n/a on the report .2.5 live conductor size and 2.5 cpc size
It may have been mentioned previously on post because there are so many bizzare entries on sheet but there are no results for your socket ring continuity. 2.5 cpc for sockets assuming it's twin and earth ?,10ka breaking capacity ?no rcd trip time ,61009 for rcd?the first 2 circuits arnt even rcbos .type of rcd ?rip it up and start again .I've never seen a circuit chart like that before ,if your going to cheat and just take the cover off the board at least make it look believable. I no way am I endorsing drive by testing just seems bizzare almost like the apps went crazy .I was told by a select advisor (there in Scotland) that some electrical bodies are actually using there own staff to check some of these eicrs in London as they suspected as much as 50 percent were completely false.sparkies get copies of previous report and change it slightly without even taking there tester out its case
Hi a rcbo is a combined mcb and rcd .it looks very similar but has a little test button on it that you press to check it's working .I guess they may search for members that do a very high number of eicrs ,especially for landlords or they may even seek out leasing agents and ask for copies of random eicrs .whether they use there own staff or contract it to a competent member im not sure ,he never went into great detail just said it was a real problem .I cannot claim that I understood everything you wrote.
What is RCBOS? And how do you identify that first 2 circuits are or aren't RCBOS
My original post contains the second report commissioned with a registered electrician. We have lost hope that we will find a competent person to do third report for us.
You might be right when you say 50% reports are fake. Where can they access previous report? Is there a portal that they can download past report from?
A long time ago an incident happened on a site I was on where one of the guys left a live cable dangling from wall,a small child recieved an electric shock and boy did select go to town.they went round nearly every job ,checked up in lofts ,under floors to see if cables were run and secured safely ,checked all test sheets going back weeks and actually made sure results matched up (roughly] to what had been recorded. So they do get involved but that's only when something goes wrong .I cannot claim that I understood everything you wrote.
What is RCBOS? And how do you identify that first 2 circuits are or aren't RCBOS
My original post contains the second report commissioned with a registered electrician. We have lost hope that we will find a competent person to do third report for us.
You might be right when you say 50% reports are fake. Where can they access previous report? Is there a portal that they can download past report from?
Reply to Review of EICR in the UK Electrical Forum area at ElectriciansForums.net