As a matter of interest, what is the size of the TX or TX's that's feeding this main switchboard, and what KA rating has the Hager DB MCCB and MCB's have??
A good point E54! I would be very dubious about this set up.
Now you've got me worried.
Engineer 54, you queried me stating this was a PME system in another thread and you have got me thinking.
I don't know the characteristics of the transformer. I have just called the DNO and they want me to e-mail them with my request, which I will do so shortly.
The premises used to be a factory and needed a lot more power than it currently does. The place is currently used as a warehouse and apart from the roller shutters and a 3 phase socket, it needs power for lights and sockets (and an immersion heater).
I said it was a PME system because this is written on a crimped off panel in the switch room. However, there are three and a half cores (seven cables) and an earth cable going back from the switch room to the transformer. This is beyond my knowledge but if I hadn't have seen 'Protected multiple earths' on the panel under the MCCB I would have assumed it was a TN-S system.
The d/b I replaced was used for the lights and socket in the switch room, I suppose the switch room got its own dedicated way so that electricians could still work there when the other d/bs and busbars were switched off.
The power supply to the fire alarm was, until I changed it, a 30A isolator with 1.5mm singles going back to a d/b, the line being wrapped around a screw on a busbar! Fused at 200A! I decided to run the power supply back to the switch room so that there was minimal chance of the fire alarm power supply being tripped somewhere else.
Now to the board I put in. The switch room unit has a 1600A MCCB and several busbars and d/bs coming from this fused at 315A for the busbars and 200A/160A/63A for the d/bs (all BS88s). The board I replaced has a 25mm 4 core fused at 3X63A. I did not put a MCCB on it, I used a 125A switch. Is this wrong? I used 10KA mcbs, this was the highest I could get.
When calculating diversity, I thought that the 63A BS88 fuses (and 100A fuses later if I change them) would not go before the mcbs on the Hager, looking at their respective curves. Consequently the fire alarm power supply and any sub board I feed from it would not be tripped by something else on the board.
Please let me know if you've seen any errors.