evening all - I have a question for some of the more learned members, I am currently trying to make a landlord understand that her rewirable fuseboard isn't up to date, so I know that in 1991 the 16th was launched meaning it wasn't to regs but I was wondering if there was any requirements in the 15th for MCB or if it just stopped being compliant in the 90's. doesn't really matter as she missed the change in regs by 25 years anyhow but it just made me wonder.
Thanks in advance for all the comments!:wink_smile:
 
evening all - I have a question for some of the more learned members, I am currently trying to make a landlord understand that her rewirable fuseboard isn't up to date, so I know that in 1991 the 16th was launched meaning it wasn't to regs but I was wondering if there was any requirements in the 15th for MCB or if it just stopped being compliant in the 90's. doesn't really matter as she missed the change in regs by 25 years anyhow but it just made me wonder.
Thanks in advance for all the comments!:wink_smile:

Is it unsafe then?
 
The installation is potentially unsafe, sink is not earthed 2 extension leads from a double socket under the sink old MK light switches, property is looked after by B.Gas and landlord maintains its fine and I am advising an EICR so I can point out the potential dangers and recommendations to upgrade. I just like to make it clear that the non compliance isn't a resultant in the change of regs last Tuesday but years of 'it all works fine'
 
The Wiring Regulations are not retrospective. If they were, every house in the country would have to be changed/modified every time a new version of the regs came out!

As above, if it met the regs at the time it was installed, then nothing needs to happen to it.

HOWEVER, if you were, perhaps, asked to add a new circuit to that board, you would have to do that work to meet the current wiring regulations. That may require the fuseboard to be changed/modified.
 
The installation is potentially unsafe, sink is not earthed 2 extension leads from a double socket under the sink old MK light switches, property is looked after by B.Gas and landlord maintains its fine and I am advising an EICR so I can point out the potential dangers and recommendations to upgrade. I just like to make it clear that the non compliance isn't a resultant in the change of regs last Tuesday but years of 'it all works fine'

What non compliance anyway?
 
The Wiring Regulations are not retrospective. If they were, every house in the country would have to be changed/modified every time a new version of the regs came out!

As above, if it met the regs at the time it was installed, then nothing needs to happen to it.

HOWEVER, if you were, perhaps, asked to add a new circuit to that board, you would have to do that work to meet the current wiring regulations. That may require the fuseboard to be changed/modified.


so as long as it meets the regs it was installed under and nothing new has been added you would call it satisfactory when you inspected it?
 
The installation is potentially unsafe, sink is not earthed 2 extension leads from a double socket under the sink old MK light switches, property is looked after by B.Gas and landlord maintains its fine and I am advising an EICR so I can point out the potential dangers and recommendations to upgrade. I just like to make it clear that the non compliance isn't a resultant in the change of regs last Tuesday but years of 'it all works fine'

Oh dear. Do you really know enough to carry out an EICR??

Why would you "earth" a sink? A decade or so ago one had to cross bond the H&C pipes in a kitchen, but that was removed several editions ago.

What is wrong with the extension leads? the load is limited to 13A in the plug. Not the best way of distributing a load, I would agree, but they are not part of the fixed wiring.
Some advice should be given if they were powering a washing machine and tumble dryer perhaps.

Note that since Amendment 1, BS7671:2008 non-compliances with the requirements of the current edition of BS7671, that do not give rise to danger or NEED improvement, do not require reporting in an EICR.

Reading this may help your understanding. http://www.----------------------------/mediafile/100404922/Best-Practice-Guide-4-Issue-4.pdf
 
Oh dear. Do you really know enough to carry out an EICR??

Why would you "earth" a sink? A decade or so ago one had to cross bond the H&C pipes in a kitchen, but that was removed several editions ago.

What is wrong with the extension leads? the load is limited to 13A in the plug. Not the best way of distributing a load, I would agree, but they are not part of the fixed wiring.
Some advice should be given if they were powering a washing machine and tumble dryer perhaps.

Note that since Amendment 1, BS7671:2008 non-compliances with the requirements of the current edition of BS7671, that do not give rise to danger or NEED improvement, do not require reporting in an EICR.

Reading this may help your understanding. http://www.----------------------------/mediafile/100404922/Best-Practice-Guide-4-Issue-4.pdf

having been out to properties where sinks have potential and giving a little discharge every time the tenant washes up I like to test their potential especially when I am called into a tenant complaining of minor shocks from the cooker.

extension leads under the sink are perfectly fine, especially in managed properties where 3 or 4 tenants live and will regularly put every appliance on in the morning when getting ready for work.

with regard to carrying out inspections I just write down whatever and recommend the landlord get a quote from some new English people to do a budget rewire and charge ÂŁ400 quid for the privilege
 
If I can buy one, I can still legitimately install a "re-wirable" board tomorrow into an install as BS3036 fuses are still current under BS7671, as long as my circuit design meets the other requirements of BS7671:2008+A3:2011, & I bet you I can design an install that will meet these requirements using a BS3036 re-wirable board.
 

Reply to rewirable fuses in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
321
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
848
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
971

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top