Rewire Issues - Advice Needed | Page 2 | on ElectriciansForums

Discuss Rewire Issues - Advice Needed in the UK Electrical Forum area at ElectriciansForums.net

Joined
Oct 11, 2018
Messages
4
Reaction score
0
Location
Cheshire
I recently had the house (3 bed semi) rewired and have come across some things that are causing me concern. I’ve made the Electricuan aware but have not yet had a proper response so I just want to get some alternative “expert” opinion.

Basically three issues.
1. The upstairs and downstairs sockets are now fed by an MCB, Type B rated 16A. I’m of the opinion these are probably too small and should be at least 20 if not 32A? For info we have 16 x 13A sockets downstairs alone. The reason ( I think) for it being 16A is explained below.
2. Downstairs, instead of rewiring a 60 year old property as a ring main, the Electrician has connected the sockets as radial spurs and fed them with 2.5mm cables from the ceiling void. Hence, I think, the reason why the breaker is only 16A? I don’t know why they were not run as a ring but shouldn’t the cable be at least 4mm, thus allowing a biggger MCB?
3. There was a single 13A socket which we had an extension block connected too, feeding tv, sky box, dvd etc. I wanted this changing to 4 new sockets (two doubles) to get rid of the extension block. The Electrician has also wired this as a spur and a spur off a spur, all run again in 2.5mm.

What are your thoughts on this and what would be your advice?
 
A note on point 3 - a spur, and rules on spurs from spurs etc only really apply to ring final circuts. This is because the protective device is sized for overload protection of two cables in parralel (each leg of the ring) and a spur wired in a single cable from this point would not be suficiently protected from overload.

A radial circuit (it sounds like this is what you have) can be split and branched off at any point, providing it is not overloaded.

Do you have 2 16A circuits? One for upstairs and one for down? If you have a seperate 3rd circuit for the kitchen (idealy 32a) you will probably have no issues with overloading. Things that could cause problems would be large loads such as heaters, tumble dryers, irons and possibly vaccum cleaners. But this should have all been considered as part of the design process.
 

Reply to Rewire Issues - Advice Needed in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
380
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
956
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
What is the distance from the point outside the house to the shed?
Replies
8
Views
783
  • Question
I have to agree with Baldelectrician on almost everything he says except one ! I wouldn’t be walking away I’d be running lol. Definitely if your...
Replies
13
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top