Good day all,
I'm writing from the Commonwealth of Dominica (NOT Dominican Republic) where we have single phase 230V, 50Hz.
I'm managing a property where the owner purchased a generator from the US and asked for it to be wired accordingly along with a Auto Transfer Switch. I've attached some pictures of name plates, invoice etc.
It seems to me the generator itself isn't wired appropriately for the 230V/50Hz we use here.
first problem that's evident is, when generator is feeding power to the house I get approx. 115V from Ground to L and 115V from Ground to N. at outlets. As you can see in the transfer switch photo they have brown 115V on one side and blue 115V on the other side, this is coming from the generator obviously, and obviously wrong..
Second problem is, if I try to put generator in AUTO it always immediately tries to start as the transfer switch sees wrong current from the grid.
What I'm looking for is some insight of what is wrong with the system as it is (I believe the genie needs to have the internal connections modified from double delta) and how to steer the local electricians in the right direction.
Thanks in advance for any help
Don
I'm writing from the Commonwealth of Dominica (NOT Dominican Republic) where we have single phase 230V, 50Hz.
I'm managing a property where the owner purchased a generator from the US and asked for it to be wired accordingly along with a Auto Transfer Switch. I've attached some pictures of name plates, invoice etc.
It seems to me the generator itself isn't wired appropriately for the 230V/50Hz we use here.
first problem that's evident is, when generator is feeding power to the house I get approx. 115V from Ground to L and 115V from Ground to N. at outlets. As you can see in the transfer switch photo they have brown 115V on one side and blue 115V on the other side, this is coming from the generator obviously, and obviously wrong..
Second problem is, if I try to put generator in AUTO it always immediately tries to start as the transfer switch sees wrong current from the grid.
What I'm looking for is some insight of what is wrong with the system as it is (I believe the genie needs to have the internal connections modified from double delta) and how to steer the local electricians in the right direction.
Thanks in advance for any help
Don