REWIRING Small 3 bed house. | Page 2 | on ElectriciansForums

Discuss REWIRING Small 3 bed house. in the UK Electrical Forum area at ElectriciansForums.net

Joined
Oct 30, 2018
Messages
12
Reaction score
2
Location
United Kingdom
My grandson is confused by conflicting information given by contractors quoting to rewire his house, which is a small 3 bed semi.
The incoming mains and meter are located at the front of the property (external meter cupboard). The consumer unit is located in the kitchen at the rear of the property.
One contractor has quoted for an 80 amp switched fuse at the meter location and running , within the property, a T&E 16 mm cable to the consumer unit. They also want to run a separate earth conductor to the T&E cable to the consumer unit. The distance from meter to consumer is some 10 metres.
The consumer unit, as well as controlling circuits within the house, will also supply a feed to a domestic garage and garden shed situated some 40 metre from the consumer unit. The electrician proposes to run a 3 core SWA cable size 2.5 mm. to a smaller consumer unit in the garage. This unit to supply Fridge Freezer. Tumble Drier. Lights and approx three 13 amp sockets.
The confusion comes because the quotes obtained are all different. I accept that are likely to be differences with regards to labour charges but expected there to be conformity with regards to cable sizes etc and similar approaches to the installation.
Can any one clear up this confusion.
 
My Grandson is away on holiday and I can't ask him for clarification on the excellent points raised in reply to my posting.
I think the 16 mm T&E , from meter to Consumer Unit, is following the route of the current mains cable. That is; via the cavity wall at the front and under the floorboards.
Not sure if it is a total rewire or is just updating and re positioning/installing extra sockets.
The garage installation (swa cable) is new. I think the 40 mtr I mentioned is an inclusive distance from house to garage and to garden shed. The distance from house to garage would not exceed 10 mtr. I agree that the swa, for garage and garden, should be greater than the 2.5 mm swa cable mentioned i.e. 6 mm to cater for future loads.

Thanks for the comments and apologies for the vagueness of the information. I live some 200 miles from the family and it is some years since I visited the house.
 

Reply to REWIRING Small 3 bed house. in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
438
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
Pretty common for lights and sockets to get a Re-wire and the Eco7 circuits usually storage heaters /water heater to remain left as was. As for...
Replies
14
Views
2K
  • Question
What is the distance from the point outside the house to the shed?
Replies
8
Views
793

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top