Hi guys still studying hoping to take exams this year at aged 54
Question is when doing continuity of rfc to confirm if a ring is complete .
Is they a table/chart for maximum ohms readings allowed etc I understand how to do the test etc and figure of 8 so hopefully just some confirmation.
Tia guys
 
if your refer to end-end readings, there is no max. stipulated, but bear in mind (r1+r2)/4 = R1+R2, thus giving rise to Zs values compliant with 0.4sec. diss. for the MCB. generally accepted that a RFC (32A in 2.5mm) should not cover a floor area > 1oo sq.m.
 
Thanks telectrix makes sense cheers
Another quick one if you don't mind.
how do you go about if items are still plugged in and can't get to unplug ie built in appliances with no means of isolation without removal of appliance.
I'm assuming would get different results between phase and neutral lines ? Tia
 
I was always taught end to end is a commissioning test , so in theory nothing should be plugged in at this stage.
If appliances are plugged in and been live you are way past commissioning an installation
 
Hi was thinking if you were looking at adding say extras outlets then u want to check it's a rfc so for checking then and would probably have something probably plugged in
 
For a confirmation of an existing ring I would say that in general just measuring the end to end continuity of the ring conductors would show that it is a ring of some sort.
To check it is a compliant ring, such as at initial verification, would require the crossover figure 8 measurements but if this had been done at the original installation if the conductors are still continuous it is unlikely to have changed, unless you can tell there have been major changes.

However even if you were to measure the crossover line and neutral resistances with a connected load on the ring it would only lower the measured resistances slightly.
The load would be in parallel with the resistance you are measuring but would be at least an order of magnitude higher or greater and so the effect on the actual measured resistance would be negligible.
For example even a load drawing the full 32A of a ring would be a resistance of about 7Ω and so on a, say, 0.7Ω ring resistance would then make it 0.63Ω so a 0.07Ω difference at the worst case.
 
And, there won't be any appliances plugged in for your practical tests :)
 
Just post to Admin for access. Westward 10, Leesparkykent, Sparkychick will be able to help I'm sure.
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread starter

Joined
Location
Leeds
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Other
Business Name
G.Latto home improvements

Thread Information

Title
Rfc for a newby confirmation please guys
Prefix
Electrician Jobs 
Forum
Electricians Jobs
Start date
Last reply date
Replies
9

Thread Tags

Tags Tags
please rfc

Advert

Thread statistics

Created
Gary latto,
Last reply from
Pete999,
Replies
9
Views
1,645

Advert

Back
Top