Earth
Went to a job yesturday.
6.6kw 4 ring hob and 4.2kw cooker were both supplied on same 6mm on 32a breaker!! Both still using the 1mm flex pre-wired to them.
Running in another 6mm was not really a option as tenant didnt want trunking!
So kept the original 6mm and put that into supply side of 45a 2g cooker switch and a new bit of 6mm from load side to ccu, then ugraded the 1mm pre-wire to a 6mm from ccu to the hob.
Then as the 1.5mm pre-wired flex couldnt be disconnected from the cooker and there was no way a 6mm would even get in the small hole of the cooker, i left the cooker on a 13a plug and spurred off of ring with a 13a sw fused spur above work top and a single socket below for cooker to plug into to.
I know the cooker can pull u to 18a, but with diversity taken into account all the above is ok right?
Cheers
Cheers
Just one word, ....Unbelievable!!
Yes cooker should be on its own citcuit, but it was not a option clearly stated by the tenant.
The hob pulls more than the cooker, so it seemed logic to keep that on the 32a supplied with a 6mm.
The cooker only pulls 18a at full go...apply diversity.....and a fused down single socket is fine no?
Re the small flex that comes wired to the cooker, it is fixed, can not be disc and replaced with a larger cable!
So explain your unhelpful replies!
should have wired both on the 6mm circuit rather than coming off the rfc for the oven. together they'll never pull more than 32A.
To the OP. Why do you think its right that you would need to change the pre-wired flex that came with the cooker from the manufactures?
I had a similar thing this week, 7kW hob and 5.4kW oven on a 32A 6mm circuit. Diversity on cooking appliances is 10A +30% of the remainder. That leaves about 1A to play with, but it's within the regs, and safely limited. The customer got what they wanted and know it'll trip if they get carried away. They'd rather that than a new circuit went in, and it was Friday afternoon, so I was happy too.
Osg mentions that in a domestic installation a cooker up to 15kw can be connected to a 6mm 32A standard cooker circuit. Agree with the flex should of been upgraded and oven left on cooker circuit.
Seeing as 6mm cable sitting on a 30/32A MCB, will comfortably look after a 15KW cooker load!! I would say they have nothing at all to worry about!!
I think hes talking about the flex that comes with the oven when you buy it and they are designed to be plugged in, I don't see why this needs to be upgraded as it is designed and sold like this.
- - - Updated - - -
Cheers
that all sounds fine to me didn't really need to fuse it down
The flex that comes with the appliance is the manufacturers call. If you change it, it becomes your call. When that appliance goes phutt bang, and they want to have it replaced/repaired under warranty, guess what'll happen next? I know what you mean, sometimes that flex does not look right at all.
Reply to right thing re cooker and hob in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
Seen this where T&E has been fixed with a flat bend of too tight a radius.
2 3
There is no reason for an item of fixed equipment to be on its own dedicated circuit just because it is fixed equipment. There may be other...
loz2754
L