Had an RFC to test today which isn't an issue, but not 100% sure as what action to take, if any.
End to end readings were -
Line 0.52 ohms
Netral 0.60 ohms
CPC 0.87 ohms
I'm happy with the Line and CPC readings, as CPC is 1.67 time that of the line. The only reason for worrying about my neutral reading is that its more than 0.05 ohms than the line.
I've had every socket of the wall to check the connections, but there are 2 which are behind fitted furniture, so can't get access to them.
Would this be noted on the cert or is access needed to be made to the 2 hidden outlets?