When you think about it this installation should have been designed , 250 metres on a ring , way to big , ive had houses that have been large long cable runs and the calcs were to close to the mark for my liking so i installed the rings in 4mm just to get the readings to an exceptable level so realy the person doing the design of this one need to get back to the drawing board
I totally agree,But I think even with 4mm and Lennys recommended 26amps we end up with a maximum of 160metres to comply with the permitted voltage drop.I've voiced my concerns that we could be ending up with a voltage drop of 30volts.but I keep getting" there will be a very light load"I don't know if that means their design or rcbo will only be 15 amps(if that makes any difference or is permitted)
I know there is to be a wall mounted lcd tv in each of the 4 rooms on the ring...and also nothing stopping the residents plugging in their own personal kettle or suchlike...A sub dist board in a store would be the obvious way to go and also save them on cabling etc....but I'm only the numpty doing the work....All I can think of is to get their requirements in writing to protect my self from future comebacks