waitees

Hi all

just wanted to confirm as got the nic man and anything that comes up, want to be confident in the answer.

Am i right saying that the r1 & r2 reading on a reading circuit should be ruffly the quarter of the end to end readings added up ie

L2L=0.26
N2N=0.26
L2L=0.43

TOTAL = 0.95

THE R1 & r2 value should be ruffly a quarter of that total.

also another quick question on the cert it says refernce method i have looked at the bs7671 bit confused, which one is mostly used in a domestic property ?

any ideas ??:confused:
 
Hi all

just wanted to confirm as got the nic man and anything that comes up, want to be confident in the answer.

Am i right saying that the r1 & r2 reading on a reading circuit should be ruffly the quarter of the end to end readings added up ie

L2L=0.26
N2N=0.26
L2L=0.43 earth 2 earth?

TOTAL = l2l + e2e devided by 4 is your r1 plus r2 at each socket

THE R1 & r2 value should be ruffly a quarter of that total.

also another quick question on the cert it says refernce method i have looked at the bs7671 bit confused, which one is mostly used in a domestic property ?
Mostly clipped direct mate
any ideas ??:confused:[/QUOTE
 
ref method means how is the cable installed, ex ref c is clipped direct to wall not touching any insulation. ring test. end to end all 3 conductors, results are little r1 little r n and little r 2. just do more study
 
measure end to end of both cables
l - l =r1
n - n = rn
e - e =r2
cross connect l - n
(add together readings r1 + r2 and divide by 4)
this reading should be seen around ring and will become R1+R2
 

Reply to ring circuit test in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
279
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
776
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
787

Similar threads

Interesting question & always gonna get different views on this. EICR testing seems to have changed over the years & not by us the Electricians...
Replies
7
Views
1K
  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top