F

foghorn

having added a couple of sockets to a ring final circuit when doing end to end tests i have no cpc end to end any advice i have checked my new works and all cpc connections are good could well have already been existing fault any advice welcomed
 
parallel conductors not following the same route contravenes a reg. forgot which one. it's a bit like buses. they follow different routes, but they don't have conductors any more.
 
Hmm, how about finding the original problem and sorting it?

Yes that would be the ideal way forward. I was simply offering an alternative. Provided both legs are connected to the same circuit breaker, then the circuit as a whole is protected by a 20 amp device and so the continuity around the ring is not necessary so any break in no matter which conductor doesn't matter. You can call it whatever you like.
 
Yea but the point is with a healthy ring final circuit each socket is fed by 5mm - 2.5 from each leg which is matched by the cpc being 3mm(1.5mm from each leg). If the cpc is broken and the circuit is still protected by a 32A mcb then each socket is then fed by 5mm live conductors and a 1.5mm cpc - incapable of carrying the fault current.
 

Reply to ring continuity in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
259
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
749
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
738

Similar threads

  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
6K
  • Question
I had an interesting little job this morning. Three sockets in an extension were not working and haven't worked for quite some time (years). It...
    • Like
    • Winner
Replies
0
Views
674

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top