This one baffled me

Complete ring continuity on each conductor L-L ,N-N,E-E

IR - N-E : 0.00 Mohm @ 500 Vdc

split ring in middle - 50.3 Mohm on one side of ring
- 30.2 Mohm on other side !!!!!

the fault disapears on both sides when i split it ! HUH ???????

Reinstate full ring and faults reapears : ?????
 
what were your step one results LL NN EE
What were your step 2 results L1N2 L2N1 cross connections
What were your Step 3 results L1CPC2 L2CPC1 cross connections

Make sure these results are correct before IR testing

It Sounds like a neutral earth reversal somewhere
release all sockets and check connections at rear

Last resort remove all sockets seperate all cables test each piece of cable in turn
 
bet there is a junction box or socket you have missed which has the fault connected to some thing like a garage supply off the ring main and an external light full of water connected to a garage supply some where between the position where you have split the ring is a connection you have missed
 
hi there. i bet you will find that if you take the sockets off , and perform an I.R test on the sockets themselves you will find some of them down. if not there maybe dampness causing this , or you may not of unplugged everthing in the property ie an extension lead under a kitchen cupboard. hope this helps
 
good point tomo had this 2 or 3 times 2 cats had pee'd over a socket and one embarressed 23 year old slightly bevvied up had also done the same
 
LOL i have tested properties for over 19yrs every single bloody boring day. Nothing still seems to amaze me, you will never stop learning you will always get better. p.s a problem shared is a problem halved...
 

Reply to Ring fault in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
361
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
918
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
They ought to be able to check for the voltage going completely off using one MCB off at a time to confirm that. That would be my assumption...
Replies
9
Views
862
  • Question
There could also be a completely unsuitable junction box embedded within the wall and tiled over or just cables in choc blocks in old accessory...
Replies
6
Views
988

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top