Looking at the picture on #3, I expect it was plastic clips that needed a screwdriver to prise open… maybe not secure now if bent.Does it take the use of a tool to access the live connections?
Superglue would fix that
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Xmas lights in the UK Electrical Forum area at ElectriciansForums.net
Looking at the picture on #3, I expect it was plastic clips that needed a screwdriver to prise open… maybe not secure now if bent.Does it take the use of a tool to access the live connections?
That is not always the case with these type of lights.Looking at the picture on #3, I expect it was plastic clips that needed a screwdriver to prise open… maybe not secure now if bent.
Superglue would fix that
Cover secured with plastic clips, not bent nor damaged by removal. I am surprised anyone on here would consider a blob of glue to be an effective mains lead clamp. As said above, sleeved earth pin another pointer to non-standard plug, not that it goes anywhere-only a 2 core "cable". A fault leading to a fault current of a few amps would make for some pretty fireworks with a 13A fuse in the plug, also.That is not always the case with these type of lights.
Also, is the output at mains voltage? If so, is the outgoing cable double insulated?
I beg to differ. A BS 1363 plug can have a solid plastic pin for use as an Insulated shutter opening device (ISOD) on devices where such is suitable. They can of course be solid brass* however, this plug is marked BS1363/A and a BS1363 plug cannot have a partial sleeved earth pin so an Earth pin part sleeved is ALWAYS counterfeit.The plug is fine
They do though.I wonder why a counterfeiter would invent a new way of manufacturing a plug pin where they could just copy the right way
The photograph of the plug does not show clearly that the earth pin is part sleeved at the angle taken.
I wonder why a counterfeiter would invent a new way of manufacturing a plug pin where they could just copy the right way…. And to make such an change that it is an obvious tell that it is counterfeit. Their sales would drop.
You are right in saying they can place whatever mark they like on it… BS numbers, double insulated symbol… or CE instead of C E?
Look… if you are worried about it, take it back to the supplier and get your money back…. Difficult now that it’s been taken apart..
Or, take it to trading standards with your concerns. Let us know how you get on.
Otherwise, plug it in, hang it up and have a merry Christmas.
Correct, fuse is not in circuit although it is connected to live. I'm informing the supplier and telling them trading standards are being informed.I beg to differ. A BS 1363 plug can have a solid plastic pin for use as an Insulated shutter opening device (ISOD) on devices where such is suitable. They can of course be solid brass* however, this plug is marked BS1363/A and a BS1363 plug cannot have a partial sleeved earth pin so an Earth pin part sleeved is ALWAYS counterfeit.
The plug is counterfeit but marked BS 1363 why would it not be, it's counterfeit anything goes, so what makes anyone feel ok saying the rest of this device is fine to use if the plug is simply changed?
Put what ever marks you like on it. Put 'BS 1363' on a plug that is not BS1363 compliant, mark it with anything you wish, mark it as double insulated and if it should be marked such what does that now tell you?
Most will buy and not give it a moments thought, I have seen these plugs come apart leaving the pin from the line conductor live in the socket after the plug was 'removed'.
I have seen fake BS 1362 fuses, who knows what they will take under fault. On some the fuse is for show and the cables are connected direct to the pins. As I said anything goes.
What is the specification on the cables insulation?
I could go on. This item is not fine and should not be trusted but just my thoughts you have yours.
My view... Destroy it or hand it to Trading Standards.
* Brass with the BS 1363 specification copper %
Good call Sir. Seeing it more and more and many less informed than yourself are risking lives and / or fireCorrect, fuse is not in circuit although it is connected to live. I'm informing the supplier and telling them trading standards are being informed.
Reply to Xmas lights in the UK Electrical Forum area at ElectriciansForums.net