Hi all,
I would like to ask you about ring final circuit canductors and schedule of test results.
I have got dedicated ring circuit to supply kitchen appliances. Circuit is protected by mcb tybe B 32A. Then supply is split into radial circuits to supply appliances by switched 13A FCUs. What value should be recorded in schedule of test results as maximum permited Zs? Is it value for mcb- 1.37 or value for fuse 1362 13A- 2.30 ?
Also what value need to be recorded in R1+R2 value? Is it (r1+r2)/4 or measured value of R1+R2 at last point in circuit (single socket to supply appliance)?
Thank you for any help.
I would like to ask you about ring final circuit canductors and schedule of test results.
I have got dedicated ring circuit to supply kitchen appliances. Circuit is protected by mcb tybe B 32A. Then supply is split into radial circuits to supply appliances by switched 13A FCUs. What value should be recorded in schedule of test results as maximum permited Zs? Is it value for mcb- 1.37 or value for fuse 1362 13A- 2.30 ?
Also what value need to be recorded in R1+R2 value? Is it (r1+r2)/4 or measured value of R1+R2 at last point in circuit (single socket to supply appliance)?
Thank you for any help.