Ring final circuit question | on ElectriciansForums

Discuss Ring final circuit question in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Joined
Dec 20, 2015
Messages
7
Reaction score
3
When you do the continuity test on a ring final circuit and you have to connect L1 to N2 and vice versa, this assumes you know which L cable is the incoming or outgoing.

I understand that if you connect L1 to N1 and vice versa the ohm readings rise then fall as you go round the ring circuit. Why is this? I can't explain this to a friend who asked.

If the connections are done correctly the readings stay the same as you go round.

Thanks
 
Hi Peter, are you a trainee ?

The reason is that in cross connecting the line and neutral conductors you are creating a closed loop through all the live conductors. When you measure at the socket you are measuring the same loop at each point and so should get roughly the same reading.
 
Hi
Yes...in training.

I understand why they should be the same reading.

but what happens if you connect L1 to N1 and cross connect L2 to N2?

the readings change then don't they? Why is this?
 
Hi
Yes...in training.

I understand why they should be the same reading.

but what happens if you connect L1 to N1 and cross connect L2 to N2?

the readings change then don't they? Why is this?

Have a think about what you are actually measuring with the cables connected in both situations. Sorry but I'm away back to work now.

If you ask a moderator there is a great training sub forum here you can apply for entry to.
 
I Sussed it.

if you do it the correct way L1 to N2 and L2 to N1 you effectively create two identical loops. Taking a reading at any socket effectively measures the resistance across two loops of equal length in parallel.
So using the equation for resistances in parallel the resistance will be the same each time.

if you connect L1 to N1 and L2 to N2 you lose the equal loop sizes at each socket. Thus when measuring the resistance across two unequal length loops and the total resistance will change becoming higher the further you go round the ring and then falling again.

Makes sense now I have drawn it out more simply and thought of each leg of the ring as a resistor.
 

Reply to Ring final circuit question in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
301
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
813
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
869

Similar threads

Continuity of the suspect cable appears fine all cores, from this I could work out the length of it and it really doesn’t appear looking at the...
Replies
2
Views
332
  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top