You have been asked to carry out a full test on a ring final circuit. It is wired in 2.5mm single core cables. (I have made the test result values up to make things easier to work out).

You have confirmed that the ring is continuous, and your r1 value is 0.5 ohm, your rn is 0.5 ohm and your r2 is 0.5 ohm, and these readings were the expected readings for the length of the circuit. So you have established that the ring is continuous, there are no interconnections, and there are no spurs.

You are expecting your R1+R2 value to be a quarter of the r1+r2 value, so 1ohm/4 = 0.25 ohm, however when you test at all the socket outlets, you get a reading of 0.125 ohm, what have you done wrong?

Answer over the weekend.

GN3 will help you, and if you are reasonable at maths, then it should also be easy "ish" to work out.

Cheers...............Howard
 
Last edited by a moderator:
Do the trainees know that off the top of their head???? Just thought I would mention it Tel.

Also, if this was a RFC for computers it would have a 4mm cpc.

OK paul, give you that. why 4mm? as it'sa RFC , 2.5mm with hi integrity earthing is adequate, IMO.
 
The "powers that be" now demand a 4mm earth for all socket circuits designated for computers in schools etc, even if you run a RFC in 2.5mm T&E you still have to run a single 4mm for "earth leakage"!!!! Two lots of dead tests to carry out due to parallel return paths lol. The council Clerk of Electrical Works is a right :censored:
 
The "powers that be" now demand a 4mm earth for all socket circuits designated for computers in schools etc, even if you run a RFC in 2.5mm T&E you still have to run a single 4mm for "earth leakage"!!!! Two lots of dead tests to carry out due to parallel return paths lol. The council Clerk of Electrical Works is a right :censored:

I did not know this.......every day is a learning day Paul
 
if t's not in BS7671, then the "powers that be" can shove their 4mm where it hurts.
 
It is in the regs, the Clerk hit us with it a couple of years ago but I cant remember the number or section it is in. I'll have a look later for it.
 
The "powers that be" now demand a 4mm earth for all socket circuits designated for computers in schools etc, even if you run a RFC in 2.5mm T&E you still have to run a single 4mm for "earth leakage"!!!! Two lots of dead tests to carry out due to parallel return paths lol. The council Clerk of Electrical Works is a right :censored:

Hi Paul.M where is the 4mm earth info from ? thanks
 
Hi Paul.M where is the 4mm earth info from ? thanks

I'll have a look for it later today when I get back from doing an EICR, just leaving home atm. (yes I know it is Saturday, only time I have to it. Been working 60-70 hours a week for the past 3 weeks and on the bank holiday, thats the reason why I hae not been posting up questions). Thanks Howard for this one, better then what I ask lol.
 
think your man is confused with the reg. about a cpc being min. 4mm if not mechanically protected. nothing to do with PCs.
 

Reply to Ring Final Circuit testing, What is wrong. Trainees only to answer please. in the Electrical Course Trainees Only area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
346
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
885
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top