The RFC is already a bit of a thing and this is a complication of it. I was going to spell that with a b... but refrained ... As the RFC relies on distributed loads that could be a problem (?). Maybe that could be simulated by alternating outlets across the pairs (if that makes any sense). Then there's the cpc aspect. Armour is fine for that in theory, but will depend on the mcb and Zs.

Type C 32amp RCBO with Zs of 0.72 so over on Max Zs.
 
It means RFC wired in 4 core cable 4 cores to 1st socket 1 pair connected to anothe pair going to the next socket until you reach the last one where you have 2 L and 2 N, ergo a RFC wired in 4 core.
You've got it... If it had been glanded straight into the metalclad sockets and used piranha nuts it would of been better.
 
You've got it... If it had been glanded straight into the metalclad sockets and used piranha nuts it would of been better.
When you look at this type of system in the cold light of day regarding the earthing/cpc and ignore the L and N conductors the and the Armour being suitable for use as a cpc, then there isn't much difference from that to a metal conduit install. You don't run a cpc in metallic conduit you fly lead from the earth stud in the box to the earth terminal on the socket face plate, no difference in doing the same with the SWA install is there?
 
If this was a standard 4mm radial without the addition of an extra help for the live and neutral (in the form of another 2 cores to assist) maybe the collective eyebrows would not be so lifted :)
 
If this was a standard 4mm radial without the addition of an extra help for the live and neutral (in the form of another 2 cores to assist) maybe the collective eyebrows would not be so lifted :)
Wash your mouth out it is a 13A socket and MUST be a ring final;)
 
Never uses two core swa for sockets, but when i use metal clad socket ( am waiting to hear "why") but i alway take the paint off in the inside round the knockout (it reassure me)
 
Never uses two core swa for sockets, but when i use metal clad socket ( am waiting to hear "why") but i alway take the paint off in the inside round the knockout (it reassure me)
Should be done on ALL metal enclosures, where conduit or SWA installations, lost count of the number of hours I spent filing coupler ends flat, filing lock nuts, cleaning paint from enclosures, not for reassurance, but for a good contact, a lost practice these days I'm afraid.
 

Reply to Ring Final Circuit wired in 4 core SWA in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
380
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
956
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

I assume said contractor is part of a Part P scheme (NICEIC, Napit, few others..) in which case complain to them. They'll investigate (in theory)...
Replies
10
Views
911
  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top