As doing a cu change ,I have a ring final in a house with an end to end reading on r1-r2-Rn are so low that somewhere very close under a floorboard the ring must have been connected together somewhere, customer refused to pay more, so i have put in a 20amp mcb. To comply with current rating of a 2.5mm cable for a radial circuit,

What would you have done.

Regards Kurtis Randle
 
As doing a cu change ,I have a ring final in a house with an end to end reading on r1-r2-Rn are so low that somewhere very close under a floorboard the ring must have been connected together somewhere, customer refused to pay more, so i have put in a 20amp mcb. To comply with current rating of a 2.5mm cable for a radial circuit,

What would you have done.

Regards Kurtis Randle

Did you test to see if the there was a bridge connection anywhere?
 
It was end of day and they didn't want to pay for anymore, just said make it safe, i had briefly done some tests but didn't have much time, so guessing it was in a junction box. Is changing to a 20a mcb okay. Its safer than before i know that
 
Last edited by a moderator:
As doing a cu change ,I have a ring final in a house with an end to end reading on r1-r2-Rn are so low that somewhere very close under a floorboard the ring must have been connected together somewhere, customer refused to pay more, so i have put in a 20amp mcb. To comply with current rating of a 2.5mm cable for a radial circuit,

What would you have done.

Regards Kurtis Randle

I think you made a good call. Personally I think testing and verifying RFC's which are an unknown quantity is often very difficult within a reasonable timeframe and without excessive disruption. Verifying spurs from spurs etc and inconsistent continuity readings may well be beyond the scope of what it is reasonable to carry out for a CU change.Note on your EIC that the ring requires further testing because of unexpected readings and that until the ring is properly verified the rating of the OCPD has been reduced to ensure safe operation. --- covered.
 
I think you made a good call. Personally I think testing and verifying RFC's which are an unknown quantity is often very difficult within a reasonable timeframe and without excessive disruption. Verifying spurs from spurs etc and inconsistent continuity readings may well be beyond the scope of what it is reasonable to carry out for a CU change.Note on your EIC that the ring requires further testing because of unexpected readings and that until the ring is properly verified the rating of the OCPD has been reduced to ensure safe operation. --- covered.

Agree, as if the customer wont pay all that can be done is to make as safe as poss in timeframe and cover --- in EIC by noting it down and inform customer.
 
As doing a cu change ,I have a ring final in a house with an end to end reading on r1-r2-Rn are so low that somewhere very close under a floorboard the ring must have been connected together somewhere, customer refused to pay more, so i have put in a 20amp mcb. To comply with current rating of a 2.5mm cable for a radial circuit,

What would you have done.

Regards Kurtis Randle


Was the testing carried out prior to the CU change?
 
Is this an old house, e.g. 1960's? Sometimes the RFC is wired so all the socket drops are spurs from junction boxes (under floor or in ceiling) connected off what is then electrically quite a short ring. Then for a single floor, r1=0.14 could be quite a reasonable value.
 
Last edited:

Reply to Ring final end to end test in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
350
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
898
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
6K
Interesting question & always gonna get different views on this. EICR testing seems to have changed over the years & not by us the Electricians...
Replies
7
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top