M

Maxstone89

As doing a cu change ,I have a ring final in a house with an end to end reading on r1-r2-Rn are so low that somewhere very close under a floorboard the ring must have been connected together somewhere, customer refused to pay more, so i have put in a 20amp mcb. To comply with current rating of a 2.5mm cable for a radial circuit,

What would you have done.

Regards Kurtis Randle
 
If r1=0.14Ω and the the resistance for 1m of 2.5mm is 7.41mΩ then the run would be around 19m (approx) assuming all terminations are made well. I guess this could be a ring for a small kitchen.

I haven't got an exact figure for r1 in my head for when I would decrease the rating of the MCB but I think you did the right thing Kurtis. It's a shame they didn't let you do a few basic checks! But I guess they'll have to get you back if the 20A MCB keeps tripping :smiley2:.
 
Last edited:
If r1=0.14Ω and the the resistance for 1m of 2.5mm is 7.41mΩ then the run would be around 19m (approx) assuming all terminations are made well. I guess this could be a ring for a small kitchen.

If you have a r1 reading you can calculate the expected r2:-

2.5mm divided by 1.5mm = 1.67 (rounded up)

0.14 X 1.67 = 0.23 ohms. This way you dont have to estimate the length of the run and a more accurate "estimation" can be produced.

If this is a "true" RFC and you are happy that it is safe to energize. Carry out a plug in Zs at all points, deduct the Ze and compare the readings from the dead tests. This should give an indication and more information of what is going on after Kevin kitchen fitter did a JB under the tiled floor lol. (had this problem loads of times).
 

Reply to Ring final end to end test in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
352
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
901
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
6K
Interesting question & always gonna get different views on this. EICR testing seems to have changed over the years & not by us the Electricians...
Replies
7
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top