D

Deleted member 112675

I'm not sure if this is a reasonable question or so stupid it shouldn't be asked. If the latter than I apologise and hope I don't get too much negativity back.

So I want to perform the test Continuity of ring final conductors on an existing ring main. Because I'm lazy and its dark outside, could I do this whilst the rest of the CU is live?

My thoughts are to pull the MCB for that circuit and pull the earth cables from the bar out too. Then for neutral, first check the neutral bar in the CU is at the same potential as earth by using a cheap multi meter to check for continuity to earth. If good, then remove the neutrals for that circuit.

Then with both cables removed, carry out the testing as per normal.
 
Since it was so quick to do, I decided to try Wilko's kind suggestion. I've only done the easy first part partly because I know it is a ring (its in my house and I've seen it) and partly because I just wanted a sanity check before doing a load of other work and then a final test.

Anyway, the numbers around the ring in ohms were:
L 0.18
N 0.17
E 0.41

This is 2.5mm twin and earth.

That last reading was higher than I would expect since I think it should be around 0.3 but not sure if its anything to worry about. Perhaps my earthing terminals are not as tight as the others.
 
Since it was so quick to do, I decided to try Wilko's kind suggestion. I've only done the easy first part partly because I know it is a ring (its in my house and I've seen it) and partly because I just wanted a sanity check before doing a load of other work and then a final test.

Anyway, the numbers around the ring in ohms were:
L 0.18
N 0.17
E 0.41

This is 2.5mm twin and earth.

That last reading was higher than I would expect since I think it should be around 0.3 but not sure if its anything to worry about. Perhaps my earthing terminals are not as tight as the others.

The 2 most likely reasons for the discrepancy from the x1.666 ratio are:
  • The cable is over 40 years old, and still had a 1mm earth with the 2.5mm live cores.
  • There is at least one case of a poor connection. Quite often you will find the result improves incrementally after reterminating the earths in each socket.
BTW, if this is the main ring circuit for the house, it appears to be quite small, and may indicate that a number of sockets (usually the downstairs ones) have been wired as spurs from a small ring. This is not a major problem, but isn't ideal for any modifications, and usually indicates an old installation.
 
Since it was so quick to do, I decided to try Wilko's kind suggestion. I've only done the easy first part partly because I know it is a ring (its in my house and I've seen it) and partly because I just wanted a sanity check before doing a load of other work and then a final test.

Anyway, the numbers around the ring in ohms were:
L 0.18
N 0.17
E 0.41

This is 2.5mm twin and earth.

That last reading was higher than I would expect since I think it should be around 0.3 but not sure if its anything to worry about. Perhaps my earthing terminals are not as tight as the others.
Your cpc will have higher resistance because the conductor is smaller.
 
i see no need to isolate a CU in the OP's case. switch off MCB. diss all 6 conductors, do dead teats on that RFC, reconnect and reset MCB, assuming dead tests are within spec.
 
Thanks very much to the majority who have given me good advice on this thread. I have nevertheless learned my lesson that talking about working live esp for a DIYer is going to annoy one or two so I shan't do that again. I do deliberately use "DIY" terms such as earth instead of CPC etc so that it is very clear I am a DIYer just in case you miss the DIY badge of shame above all my posts.

I have a lot of respect for those in many trades including electricians. DIY "bodgers" have had a terrible press of recent years in many cases with justification. The problem people face is that when you call someone out to do some work, how do you know they've done a good job? Most people are honest and will do good work even when the work is out of site but some will not. If Mrs Miggins sees her shiny new sockets & switches and they all seem to work ok how is she going to know if the installation is dangerous ? That is my motivation to DIY.

Your cpc will have higher resistance because the conductor is smaller.

Yes but not that high. It should be 2.5/1.5=1.6667 times higher but is much closer to 2.5/1 which as some have kindly suggested might indicate a 1mm conductor somewhere in the ring.

That did worry me for a short while because much of that ring was installed perhaps 20-30 years ago but I did compare the earth with a known 1mm earth and a known 1.5mm earth and it is definitely 1.5mm.

I finally resolved the issue though. Whilst the raw numbers pointed to a 1mm somewhere, I have less faith in my conductor termination skills than some of you do. So I removed all the newly added sockets one by one and connected the earths together using a wago connector (which even I can get right). As I did so I took fresh readings and sure enough the earth resistance around the ring started to come down. When I'd change all 6 I was down to 0.32 Ohms which in conjunction with the other numbers is much more consistent with a 1.5mm earth. THe problem was I simply wasn't terminating well so I went back to the drawing board, watched a couple of John Ward videos, and I plan to start looping the ends of the conductors back on themselves to fill the connector.

Thanks once again to most all of you who helped me with this.
 

Reply to Ring main continuity test in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
959
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Joining the ends of the radials together to form a ring, and changing the circuit protection to a single 32A would solve the MCB overload problem...
Replies
8
Views
780
  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top