hi my customer wants me to change her fuseboard for a 17th edition at her home.i went today to pretest the circuits and found that there was no neutral continuity on the kitchen ring and no earth continuity on the upstairs ring.My client has just had the whole house decorated and the decorators have siliconed every single socket to the very expensive wallpaper and there is wood flooring in each room.so my question is how would this get signed off with these existing faults or do i tell her that i cant do it .Any opinions?
 
Have you tested all sockets for a L N E?The earth might be broken at say socket 3 and 7 therefore leaving sockets 4 5 6 without an earth etc..Check this first before splitting into 2 radials
 
Depending on where the break is on the upstairs ring there may be the option to split the ring and alter to 2 x radial circuits.

But that then leaves the kitchen, bit more of a tricky one... not ideal splitting that one really as you've usually got quite a bit of loading in there. Maybe able trace and rewire the broken section, if its behind units, if your lucky.

Good luck
 
hi my customer wants me to change her fuseboard for a 17th edition at her home.i went today to pretest the circuits and found that there was no neutral continuity on the kitchen ring and no earth continuity on the upstairs ring.My client has just had the whole house decorated and the decorators have siliconed every single socket to the very expensive wallpaper and there is wood flooring in each room.so my question is how would this get signed off with these existing faults or do i tell her that i cant do it .Any opinions?

Tell the silly Moo, that you can't trace, test or correct anything without being able to take the wall plates off of her nice newly decorated walls. If she is silly enough to decorate first and then intend to have work done to the electrical system ...more fool her!! If she doesn't want to spoil her decoration, then walk away, you'll be glad you did!!!!

And NO you can't do a CU renewal, and leave a ring circuit in that condition, ...not unless your a cowboy sparks...

EDIT.... You don't split ring circuits into radials unless it's your LAST resort, and there is no other option open to you. All this splitting rings at the first sign of trouble smacks of, at best laziness, and at worst incompetency!!!
 
Last edited by a moderator:
Well said E54.

I can’t understand the stupidity of using silicon on any fitting. What should be a relatively simple fault is raising issues. I’ll bet a pound to a pinch of s£*t it’s the decorators that have disturbed a connection on a socket.
 
the sockets have to come off, end of!!! you could use wander lead and check to see where is broken, any recent pictures been put up , could be left hanging out by jim the decorator...

for the kitchen , socket tester will tell you where it stops.. seems a tricky one but you might get lucky.. what if main bondind needs upgrading.. just asking...
 
No, ...i don't anyway!!

It's a forum for those in the electrical industry, but now and again a member of the public comes on to ask advice. Depending on what and how he asks will generally determine whether he gets instruction advice or told bluntly to get an electrician in to sort out his/her problem...
 
Same old story people are happy to pay for something they can see like decorating or flooring but when it comes to safety and spending money on something they cant see or show to there mates there not interested.
 
thats it cj, you are correct.. i was able to convince a man today his attic needed sorted when i finished what im doing for him, recessed lights and insulation all around them .. i seen some sindging, loads of connector blocks and like a spiders web.... i said was was fire hazzard and he agreed... without looking
...
 
Exactly cjp1, we did our training and they pick our brains to save money.
Its ok when its a technical/rare problem.
Then one of us can offer advice based on previous experience but when its to instruct on simple problems its a different matter.
 
Same old same old, do the I&T, fill in the form, outline whats needed,supply a quote, agree limitations, get your fee for the I&T go home park the van have a beer, this jumping thro hoops costs you time
Pict
 

Reply to ring main fault in the Australia area at ElectriciansForums.net

Similar Threads

  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2
Replies
45
Views
5K
  • Question
Thank you bud. I’m loving this forum already being in communication with like minded individuals like yourself who can share knowledge.
Replies
4
Views
2K
  • Question
When test these disconnected cables are you also disconnecting the cpcs and only testing to them or are they still connected to the installation...
Replies
3
Views
1K
J
  • Article
Traymate Shower tray Hi guys, This is my first post so apologies if this isn't the right section for the post. I'm a qualified plumbing and...
Replies
0
Views
108
Jeefa
J
  • Question
Yea all out circuits were disconnected & Rcd ramped tested Think this will be the right way forward,with EL clamp meter Cheers have a nice Christmas 😎
Replies
2
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks