Interesting discussion!
Apologies to the original poster for derailing the post.
I think you are missing the point of the lollipop circuit ... The stick from the CU has to be a larger cable or the ocpd is too big
Yep. I know that. I don’t feel like I’m missing the point. Could one of the 2.5mm legs get overloaded if continuity in line or neutral lost around the ring part?
Anyway - definitely different opinions.
I read through the Elesca article as posted by Wilko (thank you - had not seen that before). They even quote 543.2.9 but seem to have taken it upon themselves to replace ‘having both ends connected to the earthing terminal at the origin of the CIRCUIT’ with both end being connected to the origin of the RING (junction box or smart device).
So there you have it, ELESCA suggests lollipops are compliant. My scheme assessor interprets 543.2.9 as lollipops being non-compliant.
What do I think?
I think lollipops are best avoided, but can see how they can be installed and comply with overcurrent protection.
Still thinking it through to be honest. Not quite as steadfast as I was at the start of the discussion though....
Has the original question been answered?
I was also told, as a rule of thumb, to limit cable runs to 100m, and I understand the cable calcs in terms of exceeding allowable Zs when you start getting around the 100m mark. I thought that the 100 m squared floor area maximum mentioned in the onsite guide was more to do with limiting the number of socket outlets and the probability of overload? Guesswork of course - but it kind of make sense to me.