Evening all

Has anyone ever wired a ring main in 4Core SWA and used the sheath as an earth?

Just looking at wiring some sockets in an industrial unit and wondering whether to do it that way or do a 4mm radial
 
Hi.

The list below gives the physical CSA of MICC copper sheath when its used as a cpc.

Hope it's of use.

2L1 ****** 5.4 mm2
3L1 ****** 6.7mm2

2L1.5 ****** 6.3 mm2
3L1.5 ****** 7.8 mm2
4L1.5 ****** 9.1 mm2


2H1.5 ****** 11 mm2
3H1.5 ****** 12 mm2
4H1.5 ****** 14 mm2


2L2.5 ****** 8.2 mm2
3L2.5 ****** 9.5 mm2
4L2.5 ****** 11 mm2

2H2.5 ****** 13 mm2
3H2.5 ****** 14 mm2
4H2.5 ****** 16 mm2

2L4 ****** 11 mm2
2H4 ****** 16 mm2

2H6 ****** 18 mm2
3H6 ****** 20 mm2

2H10 ****** 24mm2
3H10 ****** 27mm2

2H16 ****** 30mm2
3H16 ****** 34mm2
 
Think about it, if you have to run some tube along a long run from the DB on a nice clean wall, would you want to run Conduit from socket to socket, an\n then run another tub \e from the last socket on the run back to the DB?

Of course not, there's no need for a run back to the board, I just wouldn't wire the sockets as a ring in this situation. I would run a radial as there is no advantage to using a ring, so the disadvantages of a ring would outweigh the advantages in this instance in my opinion.
 
Why or what information do you have to back up that theory that MICC sheathing would be sufficient as a cpc for this method of wiring.
I ask because when, in the distant past we used MICC 4 core for RFCs it was a case of just use it, it was the norm to do so, can't really see any difference in MICC to SWA after all people now pay more attention to cable, and cpc sizing these days, I personally think that providing the cable is sized and installed correctly there shouldn't be a problem, bur testing will confirm, of course if you are only experienced in PVC/PVC cable all this chit chat may be of little interest, until of course you come across it in your line of expertise.
Hi.

The list below gives the physical CSA of MICC copper sheath when its used as a cpc.

Hope it's of use.

2L1 ****** 5.4 mm2
3L1 ****** 6.7mm2

2L1.5 ****** 6.3 mm2
3L1.5 ****** 7.8 mm2
4L1.5 ****** 9.1 mm2


2H1.5 ****** 11 mm2
3H1.5 ****** 12 mm2
4H1.5 ****** 14 mm2


2L2.5 ****** 8.2 mm2
3L2.5 ****** 9.5 mm2
4L2.5 ****** 11 mm2

2H2.5 ****** 13 mm2
3H2.5 ****** 14 mm2
4H2.5 ****** 16 mm2

2L4 ****** 11 mm2
2H4 ****** 16 mm2

2H6 ****** 18 mm2
3H6 ****** 20 mm2

2H10 ****** 24mm2
3H10 ****** 27mm2

2H16 ****** 30mm2
3H16 ****** 34mm2
Thanks for that Mate, will come in handy.
 
Why or what information do you have to back up that theory that MICC sheathing would be sufficient as a cpc for this method of wiring.

Generally the CSA of the sheath is over twice the CSA of one conductor in multicore MICC so will always automatically comply as a CPC.
[automerge]1567538739[/automerge]
Nave wire RFCs in 5 core FP 200 the same way as if using MICC in overseas locations, not in the UK I hasten to add.

5 core plus earth or 4 core plus earth?
 
I know you said that was in other countries, but it wouldn't comply here. BS7671 requires the cpc to be in the form of a ring with the exception of conduit/trunking used as the cpc.
I'm pretty sure this has been the way since at least the 16th edition.
Just thought I would mention it that's all, not usual to use FP for general circuits is it? nore of a safety circuit type cable I thought. could be wrong though.
 
Not sure it was just the way we used to do it on some jobs, it's basically the same way as using conduit and singles, one run of tube no return to the CU and no connectors in the socket back box, as you would use if you used 4 core SWA or MICC.
Did you have CPC's or use the conduit as the circuit protective conductor?
 

Reply to Ring main in 4Core SWA in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
426
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Joining the ends of the radials together to form a ring, and changing the circuit protection to a single 32A would solve the MCB overload problem...
Replies
8
Views
785
totally agree
Replies
12
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top