The smoothing capacitors giving you the 24Ω L-E reading as a false reading
Hi All,
While carrying out a commercial EICR today, I was doing IR testing on one of the ring mains an was getting 0.00M ohms between L/N - and the earth bar at 250V & 500V (cant distinguish what 2 earth wires belongs to the other 4 cores)
I have continuity on both L & N legs which are acceptable.
Also tested L- E bar and N - E bar both giving me 0.00M ohms
carried out a resistance test for both L & N to E bar, one was 24.4 ohms and the other was 1034 ohms
No RCD protection at all. TN-S system.
Stumped.... any suggestions on coding and where to start looking for this would be greatly appreciated.
Ok
1. 500V is the standard test voltage for pat testing, if anything can be damaged by 500V current limited to 1ma then it shouldn't be plugged in as it would fail the type testing
2. The output of a megger is current limited to about 1mA so it can't power anything.