Hi,
I'm after a little advice! I have been Carrying out a P.I.R on a old property. When testing a ring main I received a belt which did take me by surprise! After all I had just disconnected the conductors for the ring out of there terminals. So I isolated the supply and switched on one circuit at a time to identify what circuit was giving the live and neutral conductors a live feed whilst being out of the board. Found one of the lighting circuits cross feeding the ring. I have advised the customer of the problem and will require further investigation. Sorry for long winded message but I'm a little puzzled as to what could be feeding the ring? The only thing that comes to mind is obviously to start on the lighting circuit and go from there? Been back doing this work for a couple of months after doing a shift job for a number of years.:rolleyes4:
thanks in advance.
I'm after a little advice! I have been Carrying out a P.I.R on a old property. When testing a ring main I received a belt which did take me by surprise! After all I had just disconnected the conductors for the ring out of there terminals. So I isolated the supply and switched on one circuit at a time to identify what circuit was giving the live and neutral conductors a live feed whilst being out of the board. Found one of the lighting circuits cross feeding the ring. I have advised the customer of the problem and will require further investigation. Sorry for long winded message but I'm a little puzzled as to what could be feeding the ring? The only thing that comes to mind is obviously to start on the lighting circuit and go from there? Been back doing this work for a couple of months after doing a shift job for a number of years.:rolleyes4: