D
davidjones89
Advice needed on this please, testing a property today and came across a problem with ring main. End to end readings of conductors showing no continunity of line-line and cpc-cpc, neutral is showing continunity. broken ring main on two of the conductors, house is wired as one complete ring main for upstairs and down. there is evidence of alterations to property with an extension etc and the odd jb discovered under floorboards.Tested continunity at sockets by linking line/cpc at db and marked sockets with tape where readings were taken then swapped over to other leg and tested continunity of the other sockets and noted readings. checked at the back of sockets in case any of the conductors had fallen out but all seem ok. without stating the obvious about broken ring mains has anyone come across this before with the neutal the only one showing continunity, could the cable be broken withthe neutral core just still attached seems a long shot but before i start lifting carpets and floors just want to make sure i'm not missing something else